[EnergyPlus_Support] Re: Zone components of a 2-pipe system?
Thanks a lot.
The Central AHU has a heat recovery component, which receives the
return airflow from more than 1 zone, so I think I should keep the
two levels of the heating/cooling process?...as opposed to letting
the fan-coils addressing the full thermal load?...
In this case, it appears it wouldn't actually be easier to treat the
heat recovery by "manual" post-processing?...Or are there any known
downsides to this two-level approach?
At the moment, is there any approach in E+ that would accurately
mimic the system I described? I mean, could I actually (with nore or
less "manual work"), set up both a heating and a cooling coil to act
on the supply air, at zone level, setting both coils operation to
depend on the zone thermostat (at the moment, I don't really need
many details on this, I would just like to know the possibilities)?
Again, thanks a lot,
Ana Rui.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> If I am understanding the system correctly, the simplest approach
would be to
> use the 4-pipe fan coil with mutually exclusive schedules for the
heating and
> cooling coils. However, do not set the inlet conditions to be from
the central
> ahu, simply let the fancoil unit carry the entire load.
>
> It is not clear to me whether it matters that the heaitng/cooling
be modeled in
> two parts. If it does matter, then I would still use the 4-pipe
fan coil, but
> with no outside air. And then describe a constant volume air loop
which
> delivers the partially conditioned outside air using a direct air
terminal unit
> in each zone. If the direct air unit is listed with heating and
cooling
> priority 1, then the fan coil will pick up any remaining load.
>
> Mike
>
>
> On 26 Jan 2008 at 17:03, anarui.oliveira wrote:
>
> > Hello, all.
> >
> > I'm having a hard time to figure out the best options to model a
> > specific 2-pipe HVAC configuration...
> >
> > Any ideas about which could be the simplest way to approximate
the
> > zone level model of a 2-pipe (constant volume) system with:
> > - an AHU that delivers 100% OA at inermediate heated/cooled
> > temperatures (18/27 ºC) to the zone level,
> > - where a battery with either hot or chilled water coil (mutually
> > exclusive at any given moment, and necessarily in the same
operation
> > regime - heating or cooling - serving the central AHU) meets the
> > additional load (when needed),
> > - raising/decreasing the air temperature of the supply air loop
to
> > design Temperatures of 35ºC(heating) or 16ºC (cooling), to meet
Room
> > Air setpoint conditions according to a 20-25ºC thermostat?
> >
> > The "Single Duct:Const Volume: Reheat" and "Single Duct:Const
Volume:4
> > pipe" don't quite seem to reproduce this behaviour?...
> >
> > No recirculating or induced air from the room actually happens in
the
> > real situation (the zone level re-conditioning is performed
directly
> > and uniquely in the air supplied by the AHU, and then delivered
to the
> > room, where the mixed model should take care of the rest)...
> > ...but perhaps, in terms of global thermal loads and energetic
> > analysis, it wouldn't be too far fetched to use
> > - "Single Duct:Const Volume:4 pipe"
> > or
> > - "direct air" and "fan coil: 4 pipe"
> > with mutually exclusive availability schedules for the coils and
> > design air inlet temperatures equal to the setpoints of AHU
supply
> > air?...
> > ... the main differences between these options being?...
> >
> > Better options?...
> >
> > Thanks in advance,
> > Ana Rui.
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/