[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] a question about ground floor calculations
It is difficult to say for sure. It depends on how large the temperature
difference is, and if the zones are controlled to different temperatures or
free-floating. One approach would be to use the average of the zone
temperatures.
Mike
On 27 Jan 2008 at 19:58, Simge Andolsun wrote:
> I am simulating a 40mx40m, 10 story high building. Each floor is divided into 5
> zones. Each zone gives different mean air temperatures. In order to calculate
> ground floor temperatures, the mean air temperature of which zone should be
> entered into slab.exe ? Should it be the core zone?...or should I decouple the
> ground floor from the ground by defining itself as the other zone surface and
> run the simulations? if so, what should be entered as the ground floor
> temperatures? Because the mean air temperature of each zone will be different
> anyway. May anybody help me?
>
> Thanks in advance,
>
>
> ---------------------------------
> Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try it now.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/