Re: [EnergyPlus_Support] PlantFlowResolver error -- "Branch flow rates out of bounds"
That is correct. By the way, you did a nice job on the school layout and
mechanical equipment selection. You should consider getting rid of those
other warnings. Here is a summary in case others know these warnings
affect the answer.
*** ===== Final Error Summary =====
*** The following error categories occurred. Consider correcting or noting.
*** InterZone Surface Areas -- mismatch
*** ..Area mismatch errors happen when the interzone surface in zone A is
*** ..not the same size as it's companion in zone B.
*** Interzone surfaces - different zones
*** InterZone Surface Azimuths -- mismatch
*** ..The azimuths (outward facing angle) of two interzone surfaces
should not be the same.
*** ..Normally, the absolute difference between the two azimuths will be
180 degrees.
*** ..You can turn on the report: Report,Surface,Details; to inspect
your surfaces.
*** EnergyPlus Completed Successfully-- 75 Warning; 18 Severe Errors;
Elapsed Time=00hr 03min 49.97sec
Josh K wrote:
>
> I just finished checking the sum of the branch flowrates against the
> sum of
> the supply branch flowrates and found them to balance (there was
> actually a
> slightly varying difference on the order of 1E-20, so I'm assuming this is
> essentially zero).
>
> So: if I understand you correctly, this is a code issue and I shouldn't
> worry -- correct?
>
> Thanks,
>
> Josh
>
> On Feb 5, 2008 9:48 AM, Richard Raustad <RRaustad@xxxxxxxxxxxx
> <mailto:RRaustad%40fsec.ucf.edu>> wrote:
>
> > I just tested your input file by adding the pump inlet node volumetric
> > flow rate as a report variable. Then I corrected the code to eliminate
> > the plant flow resolver warnings. I found no differences in the answer.
> >
> >
> > Richard Raustad wrote:
> > >
> > > It appears from the output (csv) file that the PTAC water heating coil
> > > in zone 513_computer is operating. Please disregard these warnings
> > > unless you find good reason to suspect it affects the simulation
> > > results. From the report variables you selected, you did a very
> good job
> > > of troubleshooting the warnings. These report variables confirm
> the unit
> > > is operating correctly. I did not look closely at the plant loop
> to see
> > > if the warnings indicate a problem with the flow rate through the
> plant.
> > > To check the plant operation, report out all hot water coil (and
> bypass)
> > > outlet node flow rates and compare the sum of these to the hot water
> > > pump flow rate. Also compare pump water flow rate with the boiler (and
> > > bypass) flow rate.
> > >
> > > We will look into resolving this issue.
> > >
> > > Richard Raustad wrote:
> > > > You will have to upload your file so we can take a look.
> > > >
> > > > Josh K wrote:
> > > >>
> > > >> Hi Richard/Brent;
> > > >>
> > > >> I double checked, and the heating coils are on ACTIVE branches that
> > > >> are in
> > > >> parallel with a demand bypass branch. Any other suggestions as to
> > > >> what might
> > > >> be the problem?
> > > >>
> > > >> Thanks,
> > > >>
> > > >> Josh
> > > >>
> > > >> On Feb 4, 2008 9:12 AM, Griffith, Brent
> <brent_griffith@xxxxxxxx
> <mailto:brent_griffith%40nrel.gov><brent_griffith%40nrel.gov>
> > > <mailto:brent_griffith%40nrel.gov>
> > > >> <mailto:brent_griffith%40nrel.gov>> wrote:
> > > >>
> > > >> > Check that the hot water coils are on a plant loop branch with
> > > >> "ACTIVE"
> > > >> > control and that there is a bypass in parallel with them.
> > > >> >
> > > >> > ________________________________
> > > >> >
> > > >> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com><EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > >>
> > >
> <mailto:EnergyPlus_Support%40yahoogroups.com><EnergyPlus_Support%40yahoogroups.com>
> >
> > >
> > > >>
> > > >> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com><EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > >>
> > >
> <mailto:EnergyPlus_Support%40yahoogroups.com><EnergyPlus_Support%40yahoogroups.com>]
> >
> > >
> > > >>
> > > >> > On Behalf Of josh_miarch
> > > >> > Sent: Saturday, February 02, 2008 4:57 PM
> > > >> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com><EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > >>
> > >
> <mailto:EnergyPlus_Support%40yahoogroups.com><EnergyPlus_Support%40yahoogroups.com>
> >
> > >
> > > >>
> > > >> > Subject: [EnergyPlus_Support] PlantFlowResolver error -- "Branch
> > flow
> > > >> >
> > > >> > rates out of bounds"
> > > >> >
> > > >> > I'm attempting to simulate a large, multizone building, and I'm
> > > >> > encountering the following warning message:
> > > >> >
> > > >> > ** Warning ** PlantFlowResolver: Branch flow rates out of bounds,
> > for
> > > >> > Plant Loop=PLANT, Branch=514_COMPUTER_FC_HEATING_COIL_BRANCH
> > > >> > ** ~~~ ** Conditions should be: 0.000 <= 1.517E-002 <= 0.000
> > > >> >
> > > >> > Over the course of an annual simulation, there are enough of
> these
> > > >> > warnings (>30 000) to result in a fatal error that crashes the
> > > >> > simulation.
> > > >> >
> > > >> > The branch in question is the heating coil branch for a
> > > >> > PACKAGEDTERMINAL:AIRCONDITIONER object. Both the coil and the
> > > >> > PACKAGEDTERMINAL:AIRCONDITIONER are available when these warnings
> > are
> > > >> > occurring.
> > > >> >
> > > >> > I've noticed that this error tends to occur largely in the
> shoulder
> > > >> > seasons, when there is a relatively large amount of heating
> > required
> > > >> > in the morning (as there are relatively low external
> > > temperatures, and
> > > >> > the zone thermostat switches from the the night set-back
> > temperature
> > > >> > of 16 C to 20 C), and then cooling required later in the day (as
> > the
> > > >> > combination of higher exterior temperatures and high internal
> gains
> > > >> > adds heat to the zone). Although the load on the heating coil is
> > > >> > relatively large in the morning and the PTAC object doesn't
> have a
> > > >> > field for specifying max HW flowrates, the flow that I am
> seeing to
> > > >> > coil is definitely reasonable, which makes this error more
> > > >> perplexing...
> > > >> >
> > > >> > Any help would be greatly appreciated.
> > > >> >
> > > >> > Josh
> > > >> >
> > > >> > [Non-text portions of this message have been removed]
> > > >> >
> > > >> >
> > > >> >
> > > >>
> > > >> --
> > > >> Josh Kjenner, EIT, LEED AP
> > > >> Manasc Isaac Architects Ltd.
> > > >> 10225 100 Avenue :: Edmonton, AB T5J 0A1
> > > >> 780.429.3977
> > > >>
> > > >> [Non-text portions of this message have been removed]
> > > >>
> > > >>
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu> <http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu>>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
> >
>
> --
> Josh Kjenner, EIT, LEED AP
> Manasc Isaac Architects Ltd.
> 10225 100 Avenue :: Edmonton, AB T5J 0A1
> 780.429.3977
>
> [Non-text portions of this message have been removed]
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/