I calculated them with the expressions below;
(Karava,P.,Stathopoulos,T.,Athienitis,A,K.,Wind-induced
natural ventilation analysis, Solar Energy 81
(2007)p-22)
Cd-inlet=Q/(A*V*(Cpw-Cpin)0.5=u/V*(Cpw-Cpin)0.5
Q=Airflow rate through the opening
A=Opening area
V=Reference wind speed at reference height
Cpw=Pressure Coefficient on windward facade
u=local velocity in the opening
Cpin=internal pressure coefficient, determined for a
building with two openings by;
Cpin=Cp2+(á2*Cp1)/1+ á2
large openings(windows,doors-turbulant flow)
Cp1=External pressure in front opening
Cp2=External pressure coefficient in back opening
á=A1/A2
A1=Inlet area
A2=Outlet area
For example one of my result is 1.512 for window with
no shading device in front of it;
Cp2 -0.716 Cp1 0.840 A1 0.048
A2 0.013 á 3.625 á2 13.141 á2*cp1 11.038 á2+1 14.141
Cpin=(Cp2+á2*Cp1)/(1+á2)(for large opening) 0.730
TOPLAM Q 0.056 A1 0.048
V 2.5 m/s cpw 0.827 Cpw-Cpin 0.097
(Cpw-Cpin)0.5 0.312 CDin=Q/A*V*(Cpw-Cpin)0.5 1.512
and on page 26 it says that for large opening
areas discharge coefficient values might be outside
the standard range of 0.6-1
Thank you very much for your help.
--- Lixing Gu <gu@xxxxxxxxxxxx> wrote:
> Neslihan:
>
> 2) Discharge coefficient
>
> The discharge coefficient is between 0 and 1. Could
> you let me know how you
> obtain the value above one? Do you have math and
> physics to support?
>
> 3- What is 'mass flow exponent when the opening is
> closed'?
> Here is definition extracted on page 633 from Input
> Output Reference:
>
> Field: Air Mass Flow Exponent When Opening Is Closed
> Crack flow is assumed when the window or door is
> closed. In this case, the
> value of this field is the exponent, n, in the crack
> air flow equation. The
> valid range for this exponent is 0.5 to 1.0, with
> the default value being
> 0.65.
>
> When the opening is closed, the model treats the
> opening equivalent to a
> crack. Air mass flow coefficient and flow exponent
> are used to calculate
> airflow across an opening: Mass flow rate = Air Mass
> Flow Coefficient *
> (dP)^Air Mass Flow Exponent.
>
> Thanks.
>
> Lixing
>
>
> ----- Original Message -----
> From: "neslihanturkmenoglu"
> <neslihanturkmenoglu@xxxxxxxxx>
> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Tuesday, February 05, 2008 7:55 AM
> Subject: [EnergyPlus_Support] error in drawing file
>
>
> > Hi Lixing
> > I had uploaded my file on Feb 3,2008 for which I
> had questions, hoping
> > to be answered by you:)But I forgot to ask others.
> > My first other question is; why does ofis zone2
> floor and roof seem
> > larger in the drawing? My coordinates are true.
> >
> > 2- input /output reference book tells discharge
> coefficient values
> > must be between 0-1. In my example for front large
> opening I calculated
> > discharge coefficient values greater than 1. So
> how am I supposed to
> > enter my own values.
> > 3- What is 'mass flow exponent when the opening is
> closed'?
> >
> >
> > Thank you very very much.
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any
> files to the appropriate
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open
> EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
>
>
____________________________________________________________________________________
Looking for last minute shopping deals?
Find them fast with Yahoo! Search. http://tools.search.yahoo.com/newsearch/category.php?category=shopping
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/