[EnergyPlus_Support] Re: Cooling set-point not fully achieved
That field is already set to 1, and time step in hours is set to 4.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> What you describe is not a capacity issue, it is related to the
> prediction of loads. If you add the report variable for "Zone/Sys
> Sensible Load Predicted" and set the report variable frequency to
> detailed, you will see why this is happening. Try reducing the
Minimum
> System Time Step in the System Convergence Limits object. You
probably
> will not eliminate the problem, but it should get better.
>
>
> anarui.oliveira wrote:
> >
> > What if, in a similar (heating) case, water flow doesn't reach the
> > maximum when the problem occurs, and increasing the air flow
causes
> > further departure from temperature setpoint?...(Less than about
1.5
> > times the auto-sized air flow also leads to poorer setpoint
> > tracking); reported air flow is always equal to the constant
volume
> > fan flow, and ouside air flow rate is (and must be) user
specified.
> >
> > Regards,
> > Ana.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > Then try again to manually size the coil in the problem zone to
> > twice
> > > the size reported in the eio file. Also increase the air flow
rate
> > for
> > > that fan coil unit and fan to twice the autosized value. If
htis is
> > > happening in more than 1 zone, then just pick 1 for now to test
> > this out.
> > >
> > > Then tell me what happens to the maximum zone temperature. Did
the
> > > maximum zone temperature go down? Also tell me if the water flow
> > rate is
> > > at a maximum when the zone temperature exceeds the set point.
You
> > can
> > > report "System Node VolFlowRate" for the coil water inlet node
and
> > fan
> > > coil air inlet node to easily match volumetric flow rate with
your
> > inputs.
> > >
> > > This just sounds like a sizing issue and should be easily
resolved.
> > >
> > > anarui.oliveira wrote:
> > > >
> > > > Apparently, yes, but I set it to autosize (and I think I
already
> > did
> > > > a trial with a larger, user-defined, water flow rate)...
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > > <RRaustad@> wrote:
> > > > >
> > > > > I have not looked at your input file, can you tell me if the
> > water
> > > > mass
> > > > > flow rate through the fan coil is at a maximum when the
cooling
> > set
> > > > > point is not met?
> > > > >
> > > > > anarui.oliveira wrote:
> > > > > >
> > > > > > Please forgive me for insisting, but I DO have some
urgency on
> > > > this
> > > > > > one...
> > > > > > Again, thanks for any help,
> > > > > > Ana.
> > > > > >
> > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > > <mailto:EnergyPlus_Support%
> > 40yahoogroups.com>, "anarui.oliveira"
> > > > > > <anarui.oliveira@> wrote:
> > > > > > >
> > > > > > > Hi again.
> > > > > > >
> > > > > > > I'm uploading a new file (Zone36598_cFancoil_exp),
hoping
> > that
> > > > > > someone
> > > > > > > can help me figure out why the cooling setpoints are not
> > being
> > > > > > achieved
> > > > > > > for all times when the controls are active (namely in
Zone
> > > > 36598).
> > > > > > The
> > > > > > > model consists of Fancoil units created with Compact
HVAC,
> > and
> > > > then
> > > > > > > edited in the expanded file.
> > > > > > > I tried several user-defined and sizing options, but
> > couldn't
> > > > solve
> > > > > > the
> > > > > > > temperature peaks above 25ºC.
> > > > > > >
> > > > > > > Thanks in advance,
> > > > > > > Ana Rui.
> > > > > > >
> > > > > >
> > > > > >
> > > > >
> > > > > --
> > > > > Richard A. Raustad
> > > > > Senior Research Engineer
> > > > > Florida Solar Energy Center
> > > > > University of Central Florida
> > > > > 1679 Clearlake Road
> > > > > Cocoa, FL 32922-5703
> > > > > Phone: (321) 638-1454
> > > > > Fax: (321) 638-1439 or 1010
> > > > > Visit our web site at: http://www.fsec.ucf.edu
> > <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>>
> > > > >
> > > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > > >
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
<http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/