RE: [EnergyPlus_Support] Energy storage into a wall
I did this analysis in another way.
I modeled the same cell test with internal insulation, intermediate insulation and external insulation (changing the insulation layer position) then i reported monthly and annual Heating and cooling energy demand.
For Barcelona (Spain) there is only a very low difference (below 1%)
I did the same analysis changing the internal thermal inertia (adding or eliminating a very high insulation layer on adiabatic internal walls) and there is a high influence on energy demand about 11%
Conclusion thermal inertia on external wall has not influence but in internal walls they have a higher influence.
Josep Solé
URSA Ibérica Aislantes SA - URALITA
Dirección Técnica
C/ caspe nº 17 6ªPlanta
08010 - Bareclona - España
Tel +34 344 11 00
Tel IP +34 93 344 11 36
Móvil +34 606 42 32 14
Fax +34 344 11 00
www.ursa.es <http://www.ursa.es/>
www.ursa-online.com <http://www.ursa-online.com/>
www.uralita.com <http://www.uralita.com/>
P URALITA / URSA se compromete con el ahorro de energía. Antes de imprimir este mensaje asegúrese de que es necesario.
________________________________
Aviso de confidencialidad
Este mensaje contiene información que puede ser confidencial y de uso restringido. Si usted no es el receptor deseado del mensaje (ni está autorizado a recibirlo por éste) no está autorizado a copiar, reenviar, o por otra parte, divulgar el mensaje o su contenido a cualquier otro. Si ha recibido este mensaje por error, por favor, notifíquenoslo inmediatamente y bórrelo de su sistema.
________________________________
De: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] En nombre de Michela
Enviado el: viernes, 08 de febrero de 2008 10:37
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Asunto: [EnergyPlus_Support] Energy storage into a wall
Hello!
I'm trying to evaluate the role of thermal
inertia of an exterior wall of a very simple
building in purchased air simulation. The idea is
to calculate the energy stored into and released by the wall, say DE.
For this I use "conduction into the wall, qko"
and "conduction from outside, qki", like defined
in the manual Engineering Reference page 35 and 48 respectively.
I calculate qko by summing the energy flows at
the exterior surface as it is described on page
35 of the Engineering Reference:
qasol + qLWR + qconv - qko = 0
Instead I obtain qki from the Energy Plus
outputs: "Opaque Surface Inside Face Conduction
Gain[W](Hourly)" and "Opaque Surface Inside Face Conduction Loss[W](Hourly)".
I assume the following sign convention:
qko >0 if the flow enters into the wall
qki >0 if the flow enters into the internal zone.
Then the internal energy variation of the wall in a time step is calculated as:
DE = (qko - qki) Dt
It should be that if DE < 0 the wall is loosing
energy, while if DE > 0 the wall is storing energy.
Then I expected to find that DE changes its sign
during the day, showing the heat storage and
realease. But on the contrary during the summer
period I observed that the wall always has a
negative energy variation. The wall has more loss
then gain. But, looking at the outside and inside
surface temperatures of the wall, they are not constantly decreasing.
How do you feel with this result? Did anybody
ever try a similar analysis? May you suggest any
other way to study the energy storage into the wall?
Thanks a lot for any help!
Michela
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/