RE: [EnergyPlus_Support] zone sensible cooling energy
Also request the report variable Sensible Water Cooling Coil Energy.
Then subtract Sensible from Total to get latent.
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of beyangj
Sent: Sunday, March 02, 2008 9:16 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] zone sensible cooling energy
Dear all,
I used Fan coil system in my model, and the fan coil unit provided
outside air. I want to get the real total cooling energy, and I used
the coil report variable: Total Water Cooling Coil Energy. I wonder
how I can divide the cooling energy into sensible cooling energy and
latent cooling energy. Zone/Sys Sensible Cooling Energy doesn¡¯t
accurately give the energy consumed by fan coil units, right? If so,
how can I get the sensible/latent cooling energy consumed by fan coil
system? Could you help me? Thanks in advance!
Regards,
Young
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/