[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: "Pump not the first component..."
Dear Brent,
I feel stupid for not seeing that; I think I was looking at everything
related to the pump's position in the loop and not at the pump itself.
Thank you!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent"
<brent_griffith@...> wrote:
>
> I think you are getting this error because the node names are mixed up
> in the Pump objects. The chilled water pump input object has nodes from
> the hot water loop and so the internal checks are failing.
>
>
>
>
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
> Sent: Friday, March 14, 2008 4:51 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] "Pump not the first component..."
>
>
>
> Dear EPlus Support,
>
> I have wracked my brain for hours trying to determine the source of
> the error below... to no avail. I'll appreciate your help very much!
>
> (I'll upload the file, too, just in case it's helpful.)
>
> ** Fatal ** The following pump is not the first component on its
> loop/branch: CHWTR PUMP_1
>
> BRANCH LIST,
> BrLIST_CHWtr Supply, !- Branch List Name
> Branch_CHWtr Supply Pump,!- Branch Name 1
> Branch_CHWtr Supply Chiller, !- Branch Name 2
> Branch_CHWtr Supply Bypass, !- Branch Name 3
> Branch_CHWtr Supply Outlet; !- Branch Name 4
>
> BRANCH,
> Branch_CHWtr Supply Pump,!- Branch Name
> Autosize, !- Maximum Branch Flow Rate {m3/s}
> PUMP:CONSTANT SPEED, !- Comp1 Type
> CHWtr Pump_1, !- Comp1 Name
> NodeIn_ChWtr Pump_1, !- Comp1 Inlet Node Name
> NodeOut_ChWtr Pump_1, !- Comp1 Outlet Node Name
> ACTIVE; !- Comp1 Branch Control Type
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/