[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Fwd: Outside air mixer is recirculating return flow: Why?



Good point; I meant Mixing.

Fred

Minu Agarwal wrote:
> Cross Mixing would induce air exchange( in both directions) . I would
> suggest a Mixing Obj to result in a one way air transfer from one zone
> to another.
>
>  
>
> Minu Agarwal
>
> CoSA, Buro Happold Consulting Engineers PC
> 100 Broadway 
> New York, NY 10005
> USA
> Telephone:  +1 212 334 2025
> Fax: +1 212 334 5528
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Fred Buhl
> Sent: Monday, March 31, 2008 2:56 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: [EnergyPlus_Support] Fwd: Outside air mixer is
> recirculating return flow: Why?
>
>  
>
> I suspect it is due to the exhaust fans. Have you tried using Cross 
> Mixing objects instead?
> EPlus will assume the exhaust fans exhaust the air - and will not send 
> it to another zone.
>
> Fred Buhl
>
> anarui.oliveira wrote:
>   
>> ... Apparently, it is recirculating the exact amount of airflow that 
>> I am trying to pass from some zones to adjacent zones with exhaust 
>> fans (the aim was precisely to force the return path to collect its 
>> air flow from those areas, which are not controlled). Is it related? 
>> I can't do that?
>>
>>
>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
>>     
> <mailto:EnergyPlus_Support%40yahoogroups.com> , "anarui.oliveira" 
>   
>> <anarui.oliveira@...> wrote:
>>
>> Hello.
>>
>> I have set up a VAV system, with heat recovery, and manually entered 
>> the exact same value for for all outside airflow variables and 
>> airflow variables (the "air primary loop", the "controller:outside 
>> air", the fan, the heat exchanger,... all have the same airflow 
>> defined).
>> I hoped, with this, to establish that the supply air should be 100% 
>> OA, and no return air should be recirculated, but rather become all 
>> reflief air, passing through the heat excahnger, as I had understood 
>> from previous analysis...
>>
>> Msg 9808:
>>
>> Yes. this will provide 100% outside air with heat recovery and no
>> recirculation. However, the outside air flow will never be more than 
>> the system supply flow rate. So, when the VAV terminal units reduce 
>> the total system flow rate, the outside air flow rate will be 
>> reduced to match.
>> Mike
>>
>> On 12 Jan 2008 at 1:44, anarui.oliveira wrote:
>>
>>     
>>> Hello again.
>>> If in the Compact HVAC:System:VAV I set:
>>> - Heat recovery to sensible
>>> - both the Fan Max and Min Flow rate, and both the Max and Min 
>>>
>>>       
>> Outside Air Flow rate to the same value,
>>
>>     
>>> - and Outside Air Control Type to fixed minimum
>>> do I get a system that exhausts to the outside all the return air 
>>>
>>>       
>> of the ATU, recirculating none to the inside and substituting it by 
>> outside air, at a fixed rate, but first using the return air to do 
>> sensible heat recovery?
>>
>> BUT, reporting the flow at the different nodes, I find that, 
>> although the zone return airflows add up correctly to the "air loop 
>> inlet" flow, the Outside Air Mixing Box is diverting about 37% of 
>> that return flow and adding it to the outside air flow supplied by 
>> the heat exchanger... which was causing the 2:1 limit error I was 
>> getting at the heat exchanger, altough the defined exhaust fans are 
>> not taking out nearly that much flow (in fact, I checked that the 
>> return flow is as expected, until it reaches the Air Mixer)...
>> The zone air distribution equipment is Direct Air in all zones 
>> served by this Air Loop, so there's no change in the airflow there...
>>
>> And I can't figure out what is controlling this behaviour or how to 
>> change it to the desired model...
>>
>> Can anyone help me? I'd really like to get this one working.
>>
>> Best regards,
>> Ana Rui.
>>
>> --- End forwarded message ---
>>
>>
>>
>> ------------------------------------
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov <http://www.energyplus.gov> 
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>     
> <http://groups.yahoo.com/group/EnergyPlus_Support/> 
>   
>> Attachments are not allowed -- please post any files to the
>>     
> appropriate folder in the Files area of the Support Web Site.
>   
>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
>>     
> the Documentation link and press the "search" button.
>   
>> Yahoo! Groups Links
>>
>>
>>
>>
>>     
>
> [Non-text portions of this message have been removed]
>
>  
>
> This message has been scanned by MailController
> <http://www.mailcontroller.altohiway.com/> .
>
> Click here
> <https://www.mailcontroller.altohiway.com/sr/!k!3qU3o5Nzehiet+xA7SXbz+yy
> 4V5!sEeFNZJeKlkmDPueHlPwhl1Xg4VQRsiF2y7jMaWx+XvkP4GXCSTGnwZ16EotDYlw2ltp
> l6iYS+vGtYILzTahjezxWAm5KkgzUtiFRIPmJM+M7E0VpDntI0mG3MObNKaZ586XEjgUTfYY
> PgCORK+NFgrfXP!rlqvy4IZPY7yIqPBi8JpN5ZLZA+mvOCwpikgbX>  to report this
> email as spam.
>
>
>
> [Non-text portions of this message have been removed]
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   


[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/