Re: [EnergyPlus_Support] Re: InitializeRootFinder: error
It's likely you've done this, but if you haven't: verify that you're using
the correct "Action" (ie NORMAL vs REVERSE).
Josh
On Thu, Apr 3, 2008 at 5:25 AM, JV Dirkes II <jvd2pe@xxxxxxx> wrote:
> Dear TJ,
>
> You are correct that my value was .000005 in that field (which is not
> the same as indicated by the message!), but I must be missing
> something; changing the value to 0 results in the same error.
>
> Any other insights?
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<EnergyPlus_Support%40yahoogroups.com>,
> "tjutw" <tjutw@...> wrote:
> >
> >
> > If you change the "Min Actuated Flow" in the "Controller:Simple"
> > Object from 0.000005 to 0, then the model runs well.
> >
> > Tj Ywh
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<EnergyPlus_Support%40yahoogroups.com>,
> "JV Dirkes II" <jvd2pe@>
> > wrote:
> > >
> > > Dear EPlus Forum,
> > >
> > > Can anyone give me a clue what causes the error below? It's the only
> > > error in the .err file.
> > >
> > > Thanks!
> > >
> > > ** Fatal ** InitializeRootFinder: Invalid min/max bounds
> > > XMin=5.000001E-003 must be smaller than XMax=0.000000
> > >
> >
>
>
>
--
Josh Kjenner, EIT, LEED AP
Manasc Isaac Architects Ltd.
10225 100 Avenue :: Edmonton, AB T5J 0A1
780.429.3977
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/