Re: [EnergyPlus_Support] Zone Sizing and outdoor air



It's to give the user control over how the design ventilation air amount 
is calculated at
the zone level. Different types of zones require different amount of 
ventilation; different
standards have different ways of calculating ventilation air based on 
occupancy, zone
area etc. But most ways of calculating design ventilation rates involve 
adding things up
zone by zone. It definately does not imply that there is is a zone 
ventilation unit or a
DOAS.

Fred Buhl

JV Dirkes II wrote:
> Dear EPlus Forum,
>
> I am trying to figure out why outdoor air flow is part of the Zone
> Sizing object.  I can think of only one common means for introducing
> outdoor air to a zone that would involve zone sizing.  This would be a
> dedicated outdoor air system (DOAS), in which case you would use the
> various Zone Sizing parameters for determining the entire airflow to
> the zone from the DOAS.
>
> Any other scenarios that aren't covered by the Controller:Outside Air
> object?
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   

------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/