[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Question about the initial load when turn on the chiller
For the first hour of operation:
1) does the chiller part-load ratio match for the real vs tested data?
2) does the return water temperature match for the real vs tested data?
3) does the outdoor temperature match for the real vs tested data?
4) does changing the loop volume change these results?
Rongxin Yin wrote:
>
> Hi All,
>
> Resently i did some calibration to get the baseline model by means of
> comparing the real tested data to the simulated output results. then i
> found the simulated electrical consumption of the chiller was much
> higher than the real tested data at the beginning of the operation
> hours. and about one hour later, the load profile would be normal as
> the real data. So i am not sure whether this result is ok or not. Does
> anyone meet the same question?
>
> Thanks,
> Rongxin
>
> __________________________________________________________
> Be a better friend, newshound, and
> know-it-all with Yahoo! Mobile. Try it now.
> http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
> <http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ>
>
> [Non-text portions of this message have been removed]
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/