[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: temperature gradient



thank you very much Lixing.
--- Lixing Gu <gu@xxxxxxxxxxxx> wrote:

> Neslihan:
> 
> No, it is not as simple as you mentioned. The model
> calculates wind pressure 
> first based on wind speed and wind pressure
> coefficient. Engineering 
> Reference has a section to provide detailed
> information on page 386. If you 
> use a crack component, the airflow across the
> component is flow coefficient 
> * (Pressure difference)^(flow exponent). Therefore,
> you have to know indoor 
> and outdoor pressures also. If you the
> AirflowNetwork:Multizone:Component 
> Detailed Opening, the equations used in calculations
> are provided in the 
> Engineering Reference on page 383.
> 
> Lixing
> ----- Original Message ----- 
> From: "neslihan turkmenoglu"
> <neslihanturkmenoglu@xxxxxxxxx>
> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Thursday, April 17, 2008 4:35 AM
> Subject: Re: [EnergyPlus_Support] Re: temperature
> gradient
> 
> 
> > hi Lixing
> > I wanted to make a simple calculation  to see if
> get
> > the same results in Energyplus.
> > As I said the measurements were made with specific
> > intervals. I found the areas of these intervals
> and
> > multiplied by measured velocities. I found the
> total
> > by adding all these. At last I divided this value
> to
> > total area in order to get mean velocity.
> > When I multiply mean velocity with window open
> area I
> > get volume flow rate. Is it wrong?
> >
> >
> > --- Lixing Gu <gu@xxxxxxxxxxxx> wrote:
> >
> >> Neslihan:
> >>
> >> My answers are below your questions.
> >>
> >> ----- Original Message ----- 
> >> From: "neslihanturkmenoglu"
> >> <neslihanturkmenoglu@xxxxxxxxx>
> >> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> >> Sent: Wednesday, April 16, 2008 6:23 AM
> >> Subject: [EnergyPlus_Support] Re: temperature
> >> gradient
> >>
> >>
> >> > Hi Lixing
> >> >
> >> >
> >> > I calculated wind speed profile exponent with
> the
> >> values  got from
> >> > wind tunnel measurements in front of the scale
> >> model.
> >> > In order to understand,  I change the values
> one
> >> by one in weather
> >> > station object or site atmospheric variation
> >> object, nothing changed
> >> > in the results of airflow volume flow rate 2 to
> 1.
> >> > The only change occured when I enter my wind
> speed
> >> profile exponent
> >> > to airflow network-site wind conditions object.
> >> >
> >> Your observation is correct. The wind speed
> >> calculation in the airflow
> >> network model is independent of inputs of weather
> >> station object and has its
> >> own inputs.
> >>
> >> > I understood that one exponent is for weather
> site
> >> conditions,
> >> > the other exponent is for building site
> >> conditions.Why is there the
> >> > third one with another default value in airflow
> >> network site wind
> >> > conditions?
> >> >
> >> The field of Wind velocity profile exponent in
> the
> >> AIRFLOWNETWORK SIMULATION
> >> object and the field of Exponent of Wind Velocity
> >> Profile in the
> >> AIRFLOWNETWORK:MULTIZONE:SITE WIND CONDITIONS
> object
> >> are used for wind speed
> >> calculation. Could you let me know which is the
> >> third one specifically?
> >
> >
> >
> >>
> >> > when I compare the results of energyplus with
> my
> >> manually calculated
> >> > volume flow rates, they are not the same. So in
> >> order to define the
> >> > wind tunnel conditions in Energyplus, what do
> you
> >> suggest me to do?
> >> >
> >>
> >> What is your definition of manual calculation
> >> results? If you compare your
> >> testing results, you have to ensure the input
> values
> >> used in the EnergyPlus
> >> match your testing conditions. I have no
> knowledge
> >> of convertion from wind
> >> tunnel conditions to EnergyPlus inputs.
> >
> >
> >
> >>
> >
> >
> >> > And which velocity should I enter to design
> object
> >> wind velocity
> >> > field- u mean calculated from measured data in
> >> front of the scale
> >> > model or the wind tunnel's 2.5 m/s Gradient
> >> velocity %10 Motor
> >> > velocity.
> >> >
> >> When you got the calaculated wind velocity using
> the
> >> scale model, the
> >> velocity used in weather data should be at the
> >> height consistent with the
> >> input value of Reference height for recorded wind
> >> data in the AIRFLOWNETWORK
> >> SIMULATION object.
> >
> >>
> >> > I hope you answer in a short time.
> >> > thank you very much
> >> >
> >>
> >
> >
> >
> > 
> >
>
____________________________________________________________________________________
> > Be a better friend, newshound, and
> > know-it-all with Yahoo! Mobile.  Try it now. 
> >
>
http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
> >
> > ------------------------------------
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any
> files to the appropriate 
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable.  Open
> EPlusMainMenu.pdf under the 
> > Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> > 
> 
> 



      ____________________________________________________________________________________
Be a better friend, newshound, and 
know-it-all with Yahoo! Mobile.  Try it now.  http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ

------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/