Re: [EnergyPlus_Support] Compact HVAC problems



Josh,

In COMPACT HVAC:ZONE:VAV, try setting Zone Damper Heating Action to
Reverse Action.

fred Buhl

josh_miarch wrote:
> I'm working on a one-zone model that is conditioned using the COMPACT
> HVAC VAV objects. I'm having problems controlling the supply air flow. 
>
> I did a run to determine the maximum zone air flow, divided my minimum
> required OA flowrate by this number, and then set the result (0.0976)
> as the Zone Supply Air Min Flow Fraction in the COMPACT HVAC:ZONE:VAV
> object.
>
> The problem I'm having is that the simulation, when heating, fixes the
> supply air flowrate to the zone at its minimum, even when there is a
> substantial heating load on the zone. As a result, the zone
> temperature is often well below (~4°C) its heating setpoint when the
> VAV system is running in the heating season. Changing the Zone Supply
> Air Min Flow Fraction to a higher value (ie 0.3) fixes this problem in
> that it raises the minimum flowrate to an extent that the zone
> setpoint can be met, but the system still appears to fix the supply
> air flowrate at its minimum.
>
> I'm wondering if anyone can tell me why this system doesn't vary its
> supply air flow rate as a VAV system presumably should, or if I'm
> understanding something incorrectly. I will shortly upload the model
> if anyone would like to take a look
> at them.
>
> Many thanks,
>
> Josh
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   

------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/