Re: [EnergyPlus_Support] Mixing objects assumptions
When mixing objects are used, the user is responsible for accurately
predicting the air flow into and out of a zone. Only air entering a zone
is used in the heat balance. Infiltration and mixing (into a zone) are
included in the heat balance predict step (mi and minf in Eng. Ref. Eq 2
and 5) Supply air entering a zone is included in the heat balance
correct step (msys in Eng. Ref. Eq 5). The return air leaving the zone
is assumed to be balanced based on the supply and exhaust node mass flow
rates (mixing and infiltration are not included here). You can read more
about the assumptions for balanced flow in the text near these equations
in the Engineering Reference.
anarui.oliveira wrote:
>
> Hi, everyone.
>
> I think I've read this somewhere, but I can't find it now:
>
> - When doing the heat Balance for a Zone Air volume that is receiving
> air with a mixing object, does E+ assume that an equal amount of air is
> withdrawn from that zone, for heat balance purposes?
>
> Thank you in advance,
> Ana Rui.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/