[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Heat balance model: Zone air mass



The air volume in each zone is considered constant. The air mass is:
Mass = Volume (m3) * Density (kg/m3) at temperature and humidity ratio 
from last time step

Multiply this mass by the specific heat of air (J/Kg-C) and the Zone 
Volume Capacitance Multiplier (usually equal to 1) gives the capacitance 
of air (Joules/Celcius) used in the heat balance equation. The Cz(dT/dt) 
term in equation 2 and 5.

See the source code at the end of the Zone Volume Capacitance Multiplier 
section just after equation 11.

anarui.oliveira wrote:
>
> So, the actual air mass considered for each zone is constant, based
> on zone volume and initial density conditions?
> Ana.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> <RRaustad@...> wrote:
> >
> > Equation 2 is the heat balance equation without the impact of HVAC
> > equipment. So this equation is not impacted by airflow through
> > inlet/outlet nodes in the zone. The actual air mass flow rates used
> are
> > shown in the equation as Mi (interzone mixing caused by mixing and
> > cross-mixing objects) and Minf (infiltration). Each of these mass
> flow
> > rate terms represent the mass flow rate of air "entering" each zone
> and
> > are specified by the user. The impact of the zone inlet node mass
> flow
> > rate on the heat balance is shown in Equation 5 as Msys. This is
> the
> > actual mass flow rate "entering" the zone through the zone inlet
> node
> > and is a result of HVAC system operation.
> >
> > anarui.oliveira wrote:
> > >
> > > Hi.
> > >
> > > A question about E+ heat balance model:
> > > - What is the actual air mass (I believe it is hidden in "Cz" in
> Eq.
> > > (2)?) E+ considers for each zone? Is it constant? Is it affected
> by any
> > > of the airflows that use inlet/outlet nodes or zones nodes?
> > >
> > > Regards,
> > > Ana.
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/