The OA flow rate set using the zone sizing object will be fixed for both
min and max and can not be used to model DCV. You should run a test file
to model what you intend to do with and without a Vent:Mech object. You
could performing a test with an existing example file. Use
5ZoneVAV-Pri-SecLoop Run the simulation and view the OA mass flow rate
in the csv. You will have to add a report variable to see the mass flow
rate at the outside air node (VAV Sys 1 Outside Air Inlet, System Node
MassFlowRate). Add the Vent:Mech object and repeat the test (don't
forget to add the name of the Vent:Mech object in the Controller:Outside
Air object). You can repeat this test by changing the zone sizing
objects in several ways.
Alan Jackson wrote:
>
> Richard
>
> Thank you for your help. There is one thing I am still unclear about
> from your response. Are you saying that the OA set in the Zone Sizing
> object will not adjust to zone occupancy? If so, wouldn't the Zone
> Sizing also handle DCV?
>
> Thanks
>
> -
> aj
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> <RRaustad@...> wrote:
> >
> > Your are correct in that the zone sizing object determines the minimum
> > OA flow rate when autosizing. The ventilation mechanical object is used
> > to provide demand controlled ventilation. Also notice that the flow
> > rates specified in the Vent:Mech object can not be autosized. So the
> > Vent:Mech works in conjunction with the OA system and the OA air flow
> > rates are restricted to the min/max flow rates in the OA controller..
> >
> > Alan Jackson wrote:
> > >
> > > Can someone explain or point me towards the documentation has better
> > > clarification on the way outdoor air is calculated? There are many
> > > fields within the IDF file that autosize the minimum OA and I am
> > > curious as to where these values are coming from. I initially thought
> > > that they were coming from the Zone Sizing information but then I came
> > > across the VENTILATION:MECHANICAL controller and could not distinguish
> > > between the difference in functionality at that point. I have read the
> > > I/O document and would appreciate a better understanding of how this
> > > all works outside of economizer mode.
> > >
> > > thanks
> > >
> > > -
> > > aj
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/