Re: [EnergyPlus_Support] Boiler Efficiency modeling
A new boiler model is scheduled for the next release of Energyplus. The
current model does not have a sufficient inputs to correctly model new
condensing boilers. I will discuss remaining issues with you through
direct email communication.
JV Dirkes II wrote:
>
> Dear E+ Forum,
>
> I am reviewing the E+ boiler simulation objects for their ability to
> model "real world" energy usage. My past experience with boiler
> energy use indicates that there are a number of factors, such as
> jacket and blowdown losses, which cause a boiler to be dramatically
> less efficient at part load than at full load. Some ASHRAE studies of
> actual installations show that a well-maintained boiler may achieve a
> seasonal average efficiency of less than 60%!
>
> Over 10 years ago, when reviewing some DOE2 engineering documentation,
> I took notes of the "part load factor" used by DOE2 for gas unit
> heaters and boilers, and have used that in BIN analyses. I suspect
> that new boiler control methods have made my DOE factors obsolete, so
> I am asking for information that you may have which discusses creation
> or use of part load factors in E+ that are appropriate for
> new-generation boilers.
>
> In addition, condensing boilers seem to represent a special case,
> since their efficiency varies not only with part load ratio, but also
> with the entering water temperature.
>
> Finally, a condensing boiler which has a setpoint which is reset
> according to outdoor temperatures, is even more complex.
>
> Does anyone out there have experience with modeling boilers in E+
> which account for these factors?
>
> Thanks in advance!
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/