RE: [EnergyPlus_Support] CHP simulation results
Your input object ELECTRIC LOAD CENTER:GENERATORS has a error. Because
the thermal to electric ratio is set to 0.0, the generators never come
on. The "2.444" value for this ratio needs to be in the next field up.
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of tasos.ioannou
Sent: Friday, May 09, 2008 4:06 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] CHP simulation results
Dear Forum,
We want to model the energy balance of a 30 floor high carbon neutral
building. For this we got one floor of this building and through
energy plus we are trying to see the effect of various installations
to this floor before we make the simulation for the whole building.
The simulation that we made for the CHP had some errors in the
beginning that we fixed. Despite the absence of fatal errors the
results of our simulation, from the exEso file were very strange. The
CHP is not producing any electricity and the thermal energy appears to
be negative. Also the fuel consumption LHV and HHV are zero. The file
was made in accordance to the new EnergyPlus version example. I really
cannot find out what is wrong. The SVG file seems fine and all the
objects seem to be correct.
Is there something that we are missing? I will also upload the file.
Thank you.
Regards
Tasos Ioannou
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/