Dear F,

My copy of 90.1-2004 shows Assembly Maximum "U" for a "mass"
above-grade wall = .580 and also that no insulation is required. 
Might your copy be damaged?  Are you using the proper version? (e.g.,
2004)

For the record, 

Metal building: U = .113 R=13
Steel-framed: U = .124 R=13
Wood-framed: U = .089 R=13

The "mass" U value does seem a bit out of line, but that may be caused
by the time-delay impact of the mass.  You may want to ask ASHRAE or
review some of their standards interpretations online at ashrae.org.


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "mtdagustin"
<mtdagustin@...> wrote:
>
> Dear E+ Users,
> 
> I am trying to model a non-residential building located at Zone 1 as 
> defined by ASHRAE 90.1. However, I am not sure if I have interpreted it 
> correctly. Table 5.5.1 , "Walls above grade" calls for Assembly maximum 
> (Mass) = U-3.292 and insulation R-value is not required. Comparing this 
> value with other wall systems i.e. metal building 0.642, steel frame 
> 0.705 and 0.504 is not comparable.
> 
> Could someone enlighten me on this issue.
> 
> 
> regards
> F
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/