[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Re: Pump Power calculations
Because I left out 1 important equation:
TotalEffic = 0.78d0 * PumpEquip(PumpNum)%MotorEffic
JV Dirkes II wrote:
>
> Dear E+ Forum,
>
> I've got the pump power equation figured out and am now trying to
> reconcile the data in .eio with my calcs.
>
> Per .eio:
> Rated Volumetric Flow Rate [m3/s] .0130493
> Rated Power Consumption [W] 5041.09232
>
> My calcs say it should be:
> .0130493 * 301322 = 3,932W (Note that efficiency = 1)
>
> Why is there a difference?
>
> PUMP:VARIABLE SPEED,
> HtgWtr Pump_1, !- Pump Name
> NodeIn_HtgWtr Pump_1, !- Inlet_Node
> NodeIn_Boiler1, !- Outlet_Node
> Autosize, !- Rated Volumetric Flow Rate {m3/s}
> 301322, !- Rated Pump Head {Pa}
> Autosize, !- Rated Power Consumption {W}
> 1, !- Motor Efficiency
> 0, !- Fraction of Motor Inefficiencies to
> Fluid Stream
> -0.006429, !- Coefficient1 of the Part Load
> Performance Curve
> 1.362214, !- Coefficient2 of the Part Load
> Performance Curve
> -0.348214, !- Coefficient3 of the Part Load
> Performance Curve
> 0, !- Coefficient4 of the Part Load
> Performance Curve
> 0, !- Min Flow Rate while operating in
> variable flow capacity {m3/s}
> CONTINUOUS, !- Pump Control Type
> SchCpct_AlwaysOn; !- Pump Flow Rate Schedule Name
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, "JV Dirkes II" <jvd2pe@...>
> wrote:
> >
> > Dear Richard,
> >
> > So, pardoning my ignorance of SI, if
> > %Power = %Head x %NomFlowRate / Eff
> > does that mean that m3/s x Pa = W ?? (i.e., no units conversion
> > constant? That doesn't seem right...)
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > Straight out of the sizing routine...
> > >
> > > PumpEquip(PumpNum)%NomPowerUse =
> > (PumpEquip(PumpNum)%NomPumpHead
> > > * PumpEquip(PumpNum)%NomVolFlowRate) / TotalEffic
> > >
> > >
> > > JV Dirkes II wrote:
> > > >
> > > > Dear E+ Forum,
> > > >
> > > > For ASHRAE 90.1 baseline models, a pump is limited to a specific
> unit
> > > > power (e.g., 22W / gpm for chilled water pumps). I want to autosize
> > > > the pumps, but use a Delta P and motor efficiency that will always
> > > > result in the desired unit power. My derivation of that Delta P
> value
> > > > does NOT result in the power level that I expect when I run E+. So,
> > > > either my derivation is incorrect, or E+ calculates the power in a
> > > > different manner.
> > > > Will someone direct me to the E+ power formula for situations
> when the
> > > > pump is autosized? I must be missing something, but cannot find
> it in
> > > > "Help". Thanks!
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/