[EnergyPlus_Support] Re: Purchased Air variables
Thank you.
The variations with supply temperature are actually very small, when 
I look at them in terms of percentual differences, and I suppose they 
can be overlooked as small differences in simulation conditions.
Regarding the dT and dH terms you mention, I took yet another look at 
the Engineering reference, but I'm not sure I understood it correctly:
- The "initial" or departure conditions for determinig the dT and dH 
terms are based on the "entering air" conditions (at the inlet of the 
virtual PA unit), right?
- and these are based on the recirculated air and on the outside air 
conditions?
- if no OA was defined in the PA object (instead it was defined 
independently, as a ventilation object), the departure conditions for 
dT and dH calculation are the zone conditions (recirculated air)?
Thanks again,
Ana Rui.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad 
<RRaustad@...> wrote:
>
> 2) Sorry, wrong equation - Q=M*dH
> 
> Richard Raustad wrote:
> >
> > 1) - the maximum reported heating/cooling rate increases
> > The load met by purchased air should not change IF the zone 
conditions
> > have not changed. Mass flow rate should increase. Check the zone 
> > conditions.
> > PAOutput = M*Cp*dT
> > 2) - Why, for instance, when cooling, the cooling rate/energy 
increases
> > greatly when lowering the supply humidity ratio in Purchased Air
> > definitions?
> > Since you specified a lower humidity ratio, the dH from zone 
supply
> > inlet to zone is greater. Q=M*Cp*dH. Mass flow rate should be the 
same.
> > 3) - what should be the approach to choosing the supply 
temperature and
> > humidity ratio to be set in Purchased Air objects?
> > Choose the SA temp/humrat inputs to closely resemble the supply 
air
> > conditions of the "real" system you expect to use to replace PA.
> >
> > anarui.oliveira wrote:
> > >
> > > Hello.
> > > I've been doing some experimenting with Purchased Air and I'd
> > > appreciate some help to better understand why:
> > >
> > > - the maximum reported heating/cooling rate increases as I set 
the
> > > supply air temperatures in Purchased Air to be closer to the 
zone
> > > setpoint temperatures?
> > >
> > > - Why, for instance, when cooling, the cooling rate/energy 
increases
> > > greatly when lowering the supply humidity ratio in Purchased Air
> > > definitions? Does PA actually accounts for the energy necessary 
to
> > > force the supply airflow below dew point and then back to the
> > > defined supply temperature again? I was under the ideia that PA 
was
> > > much simpler than that?... In the affirmative case, which are 
the
> > > departure conditions that PA considers to calculate those extra
> > > energy consumptions due to HR adjustments?
> > >
> > > Considering that I'm using PA for a first approach of thermal 
load
> > > estimates and equipment sizing, what should should be the 
approach
> > > to choosing the supply temperature and humidity ratio to be set 
in
> > > Purchased Air objects (especially HR greatly influences 
results)?
> > >
> > > Regards,
> > > Ana Rui Oliveira.
> > >
> > >
> >
> > -- 
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu 
<http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
    Individual Email | Traditional
<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)
<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/