Hi Marzia, I think you can model the medallions as
shading surfaces and then add reflectance properties using the Shading Surface
Reflectance object (see the documentation). This object allows for specular
(beam-to-beam) reflectance which is what I think you are looking for. It
looks like it should work with the Daylighting:Detailed calculation, but I'm
not 100% sure. You'll have to make sure you use the solar distribution
options "withReflections". One other thing to keep in mind is
that you are not going to have reflected glare all the time. My
experience is that there are only certain times of day and year where the beam
reflection will line up just right to bounce into your zone. And
depending how large the window aperture is and what time step you are using,
you might miss the reflection altogether because it is occurring between time
steps. You might want to consider using a program outside of EnergyPlus
that will do full ray tracing and daylighting analysis to study just the times of
day/year where there is a glare problem. Good luck, P From: Hi, The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.