Dear Ana,

I get excellent agreement for fan power when using (US measurements):

BHP =    CFM x    Î"P       
                  η x    6,355
               
=   f3 x    in. w.c. x    62.316 lb              x     min-HP
    min               η            ft2 x 12 in. w.c.      33,000 ft-lb
               
=    CFM x     Î"P
          η  x   6,355

It is important to know the mechanical efficiency of the fan "η" from a fan chart, or to derive it from known Brake HP.

Also, you must make sure that the E+ report reflects the correct flow. A relief fan, for example, may never operate at the rated airflow and the .eio report only shows Watts for the modeled airflow.  The .ssz will show the design airflow.
If you are using a sizing factor greater than 1.0, don't forget to use the rated airflow x sizing factor as your basis for power calculations.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "anarui.oliveira" <anarui.oliveira@...> wrote:
>
> Hi, me again.
>
> Has anyone tried to compare the E+ estimates of Fan Electric Power with
> rated electric consumptions for these equipments?
> I've been trying to "calibrate" these values, but I keep getting E+
> plus estimates much lower than supplier data (like 2 to 10 times
> smaller values, for E+ estimate of Fan electric power).
>
> Regards,
> Ana Rui.
>
__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___