For your HVAC system you need to modify the CW cooling coil control 
variable to TempandHumRat and include a maximum humidity ratio set point 
manager as shown in the example file 5ZoneWaterCooled_HighRHControl.idf.

  Controller:Simple,
    Central Cooling Coil Contoller 1,  !- Name
    TEMPandHUMRAT,           !- Control variable
    Reverse,                 !- Action
    FLOW,                    !- Actuator variable
    VAV Sys 1 Outlet Node,   !- Control_Node
    Main Cooling Coil 1 Water Inlet Node,  !- Actuator_Node
    0.002,                   !- Controller Convergence Tolerance: delta 
temp from setpoint temp {deltaC}
    autosize,                !- Max Actuated Flow {m3/s}
    0.0;                     !- Min Actuated Flow {m3/s}

    ! This object uses results from ZONE CONTROL:HUMIDISTAT and needs to 
reference the same zone

  SET POINT MANAGER:SINGLE ZONE MAX HUM,
    Space2-1 Humidistat Manager,  !- Name
    ,                        !- Control variable
    ,                        !- Schedule name
    VAV Sys 1 Outlet Node,   !- Name of the set point Node or Node List
    SPACE2-1 Node;           !- Control zone air node name


vdezes wrote:
>
> Hello energyplus team
>
> I'm curently working on a project which imply a control of temperature
> and humidity.
>
> I've tried to use example files that exist but i can't find the good
> parametric procedure to control humidity.
>
> Could somebody describe me the different steps to introduce a humidity
> control ?
>
> The idf file exported from designbuilder has been put on the "problem
> submittals file" on"humidty control"
>
> Many thanks
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/