Re: [EnergyPlus_Support] Re: Continued Heat Pump Woes



JV,

 

Thanks for your analysis!   Instead of a borefield, I'm using a cooling tower and back up boiler, but your points are well taken.  I'll try some additional adjustments.

 

Thanks again.

 

Judy

--- On Mon, 7/28/08, JV Dirkes II <jvd2pe@xxxxxxx> wrote:

From: JV Dirkes II <jvd2pe@xxxxxxx>
Subject: [EnergyPlus_Support] Re: Continued Heat Pump Woes
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Date: Monday, July 28, 2008, 11:38 AM

Dear Judith,

I have NOT used that heat pump system. Your errors, though, suggest that:
1) You do not have enough capacity to get rid of heat. The high
pressure / high inlet side temp error probably occurs in the fall or
late summer when you've spent the previous month or so adding heat to
the borefield and the surrounding earth is now warmed up and unable to
take any more energy.
2) Perhaps the borefield is just too small and the same problem is
occurring in the winter. The theory would be that not only do you
overheat it in the summer, but cool it too quickly in the winter.

That's my "Armchair quarterback" opinion of the day. Hope it helps!

--- In EnergyPlus_Support@ yahoogroups. com, Judith Peters
<jdth_peters@ ...> wrote:
>
> Dear Forum,
>
> I am still having difficulty with water-to-air heat pumps and am
running up against a deadline.
>
> I get the following error messages:
>
> Warning ** WaterToAir Heat pump:cooling [HEAT PUMP COOLING MODE
AHU4] shut off on high pressure > 4000000
> ************ * ** ~~~ ** This error occurred 30541 times.
> ************ * ** ~~~ ** Max=63.178048
SourceSideInletTemp [C] Min=55.560386 SourceSideInletTemp [C]
> ************ *
>
> ** Warning ** GetDensityGlycol: Temperature is out of range (too
low) for glycol density
> ************ * ** ~~~ ** This error occurred 38283 times.
> ************ * ** ~~~ ** Max=-1.863618E- 002 {C}
Min=-3.581789 {C}
> ************ *
> ************ * ** Warning ** GetSpecificHeatGlyc ol: Temperature
out of range (too low) for glycol specific heat
> ************ * ** ~~~ ** This error occurred 72132 times.
> ************ * ** ~~~ ** Max=-1.863618E- 002 {C}
Min=-3.581789 {
>
> I don't have any severe errors, but I have several hundred thousand
warnings and results that are not logical.
>
> Thank you.
>
> Judy
>
>
>


__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___