[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Variable Speed Fan
Dear Forum
I still cannot make the variable fan to run at different speeds. Does
anybody has an example where this happens? Maybe if I take a look I
can see what I am missing.
Regards
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jvd2pe" <jvd2pe@...> wrote:
>
> Dear Elreq,
>
> Assuming that you are using one of the constant volume fan objects....
>
> Constant volume and constant pressure = constant power.
>
> Normally, the variation in outdoor air is accomplished by a mixing box
> ("Mixer" object in E+), which just adjusts the ratio of outdoor and
> return airflows.
>
> If you are using a variable volume fan, something is forcing th fan to
> remain at constant volume.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Elreq" <tolteca33@> wrote:
> >
> > Thanks for the recommendation but I obviously read all this.
> >
> > Now I have a big question because I have created a schedule for the
> > minimum outside air flow, depending on the occupancy, and in the
> > results it clearly shows that the air changes per hour on each zone is
> > not constant anymore, being higher in the hours of occupancy, but the
> > supply fan, that is supposed to provide this outside air, is always
> > running at the same power. So I dont know how is possible that the air
> > flow is changing but the fan is always running at the same speed.
> >
> > Any suggestions greatly appreciated.
> >
> > Santiago.
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@>
> > wrote:
> > >
> > > Dear Elreq,
> > > I recommend that you review the Input Output Reference, starting at
> > > page 1162. Several fans are discussed. In short:
> > > Fan:Simple:Const Volume is a constant volume, continuous
operation fan
> > > which can be turned on and off via a schedule.
> > > Fan:Simple:OnOff is similar to the one above, but it cycles
itself on
> > > and off as required by its thermostat ... all during the scheduled
> > > operation period. This is a typical mode of operation for a home
> > furnace.
> > > Fan:Simple:Variable Volume runs continuously during the Schedule
> > > period, but varies its volume to meet the heating or cooling demand.
> > >
> > > I hope that this is helpful!
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Elreq" <tolteca33@>
wrote:
> > > >
> > > > Dear Forum,
> > > >
> > > > I am simulating a typical house with balanced ventilation and
> > > > baseboard heating units. I want that the supply fan of the Air
Loop
> > > > has three different speeds, so I introduce the fan coefficients
> > > > mentioned in the input output reference that correspond to the
> > > > variable speed motor. The problem is that the fan is constant
> all the
> > > > time at a constant speed. Could somebody tell me how to make
it work
> > > > as a variable speed fan?
> > > >
> > > > Many thanks.
> > > >
> > >
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/