[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] DSF



1    DSF model

When the AirflowNetwork model is used, airflow rates can be calculated due 
to pressure differences. However, cavity convection is not simulated 
correctly. The airflows calculated using the model are a part of zone energy 
balance only. Therefore, the model is not correct to simulate DSF. I am not 
sure which window model is used for the other approach.

2    Mass balance

Mass conservation is based on a zone (all incoming flows = all outgoing 
flows), not a component. Please look at the Pressure and Airflow 
Calculations section of Engineering Reference on page 379.

Best regards,

Lixing Gu
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Phone: (321) 638-1411
Fax: (321) 638-1439

----- Original Message ----- 
From: "creamy_1023" <creamy_1023@xxxxxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, July 28, 2008 8:04 AM
Subject: [EnergyPlus_Support] DSF


>I have two questions about double skin facade model.
>
> 1. I input the DSF as a separate zone. In a DSF, there should have two
> opening to let the air flow in and out. I had input the opening as two
> methods. The first one is add two windows in Heat transfer surface:sub
> on the surface of DSF. The second one is add two opening in Airflow
> Network: Detailed Opening Component on the surface of DSF. But they
> have two different results of volume flow rate. Which one is correct??
>
> 2. Also, the airflow rate from node 1 to node 2 (inside to outside) in
> DSF should be equal to the airflow rate from node 2 to node 1 (Outside
> to inside), because of the conservation of mass. However, they are not
> equal. It's there any reasons??
>
> Thanks!
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate 
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the 
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
> 


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/