You can only use a gas or electric heating coil in the 
Furnace/UnitarySystem objects. A gas, electric, or desupheating coil can 
be used as the reheat coil in Furnace/UnitarySystems when humidity 
control is required. For a cooling/heating system use the 
DXSystem:AirLoop with a hot water or steam heating coil downstream. See 
example file SteamSystemAutoSize.idf. For a heating only system, I think 
you can use only a hot water or steam coil in the air loop.

D T wrote:
>
> Thanks for the suggestions. I created a Coil:Steam:AirHeating object 
> and connected it to the Furnace:HeatOnly object. However, I am having 
> problems connecting the Furnace to the boiler. I read the error 
> messages I am getting and I still cannot figure out how to fix the 
> problem. Apparently I am having a problem with the branches and nodes. 
> I created an AirLoop for the steam boiler. More or less, I am having 
> trouble figuring out how to correct my errors. Any help or suggestions 
> are appreciated.
>  
> Thanks,
> Dimos
>  
> P.S. I've uploaded my file.
>
>
> --- On *Mon, 8/4/08, JV Dirkes II /<jvd2pe@xxxxxxx>/* wrote:
>
>     From: JV Dirkes II <jvd2pe@xxxxxxx>
>     Subject: [EnergyPlus_Support] Re: need help w/ monthly gas usage
>     results
>     To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>     Date: Monday, August 4, 2008, 9:07 PM
>
>     Dear Dimos,
>
>     I took a look at the new file, and it appears that:
>
>     1) You have two air loops. Each of those has a Furnace:HeatCool. One
>     of the furnaces has a gas heating coil and the other has an
>     electric coil.
>     2) You have a "Boiler:simple" (which is a hot water boiler) and a
>     "Boiler:Steam" , but the only thing using either one is the Fan
>     Coil in
>     Zone 1405.
>     3) Therefore, neither of the Furnaces will use any energy from the
>     Boilers because they're not using hot water or steam coils. In
>     addition, the Boiler:Steam will not use any gas, because it has
>     nothing connected to it.
>     4) If the Fan Coil has any load, the Boiler:Simple will provide it ...
>     as long as the Boiler is available and the Fan coil operates.
>     5) Finally, you have created a Gas Equipment object called "Boiler",
>     but it is not connected in any way with the heating loads, and
>     therefore is not useful to you.
>     6) I think you should:
>     a) Delete the "Boiler" Gas Equipment object. This is not the correct
>     approach for a heating load.
>     b) Connect the heating devices (Fan Coil or Furnace, whichever is
>     proper) to the Boiler:Simple or Boiler:Steam. If you use
>     Boiler:Steam, you'll need a Coil:Steam:AirHeati ng object in the
>     Furnace or Fan Coil.
>     c) Check the Fan Coil operation and confirm that it operates and also
>     has some heating to perform. Also check to see that the Boiler:Simple
>     is operating when you need it.
>
>     That's all I can figure out right now. Good luck!
>
>     --- In EnergyPlus_Support@ yahoogroups. com
>     <mailto:EnergyPlus_Support%40yahoogroups.com>, D T <ellinas.1984@
>     ...> wrote:
>     >
>     > Thanks for the help. I modeled the ovens using the GAS EQUIPMENT
>     object as well as the boiler. I did this in order to get monthly gas
>     usage values for one entire year for the entire faclity. They closely
>     matched the faclity's gas bills. For the boiler, I used the GAS
>     EQUIPMENT object because I had some problems using the STEAM BOILER
>     object in EnergyPlus.
>     >
>     > I specified all the inputs in the STEAM BOILER object yet I don't
>     get any monthly output results. I do not know why I am not getting any
>     values for the steam boiler. Do you know why this could be happening?
>     Also, I have yet to specify the fans for the ovens. But, I would like
>     to ask, under which object in the Fans category of EnergyPlus would I
>     use to model the fans?
>     >
>     > Thanks again for the help. I will upload my idf file.
>     >
>     > Dimos
>     >
>     > --- On Fri, 8/1/08, JV Dirkes II <jvd2pe@...> wrote:
>     >
>     > From: JV Dirkes II <jvd2pe@...>
>     > Subject: [EnergyPlus_ Support] Re: need help w/ monthly gas
>     usage results
>     > To: EnergyPlus_Support@ yahoogroups. com
>     <mailto:EnergyPlus_Support%40yahoogroups.com>
>     > Date: Friday fan for circulation; the energy for these fans should
>     > be included in your model.
>     >
>     > --- In EnergyPlus_Support@ yahoogroups. com, D T <ellinas.1984@ ...>
>     wrote:
>     > >
>     > > Thanks for the suggestion. Since I have never modeled boilers nor
>     > ovens in EnergyPlus, could you perhaps steer me toward the objects I
>     > would need to work with. I know that for boilers there are several
>     > objects. The plant I am modeling uses boilers for steam
>     generation, so
>     > would I need to use the steam boiler option? Also, for the
>     ovens, what
>     > object do you suggest I work with?
>     > >
>     > > Assuming I get these to work properly after modeling them, how
>     would
>     > I get them to report in the ABUPS report?
>     > >
>     > > Thanks in advance for helping me with this.
>     > >
>     > > Dimos
>     > >
>     > >
>     > >
>     > > --- On Thu, 7/31/08, JV Dirkes II <jvd2pe@> wrote:
>     > >
>     > > From: JV Dirkes II <jvd2pe@>
>     > > Subject: [EnergyPlus_ Support] Re: need help w/ monthly gas usage
>     results
>     > > To: EnergyPlus_Support@ yahoogroups. com
>     > > Date: Thursday, July 31, 2008, 8:08 PM
>     > >
>     > >
>     > >
>     > >
>     > >
>     > >
>     > > Dear Dimos,
>     > >
>     > > The Boiler and ovens will operate on different schedules with
>     > > different loads and will have different part load efficiencies.
>     > > Therefore, I think you should model them separately, not as a
>     combined
>     > > object.
>     > >
>     > > I have not modeled ovens before in E+, but I have applied them in
>     > > buildings. A typical oven will lose heat to the zone it occupies
>     > > through the oven walls, so you'll need to know the insulation
>     value of
>     > > those walls and calculate that rate. The rate will vary as the
>     oven
>     > > warms up and cools down, so you will need to know the operating
>     > schedule.
>     > >
>     > > An oven also loses heat through the stack. That is the amount
>     which
>     > > should be assigned to the "Fraction Lost" field.
>     > >
>     > > --- In EnergyPlus_Support@ yahoogroups. com, D T
>     <ellinas.1984@ ...>
>     > wrote:
>     > > >
>     > > > Thanks for the help. I now understand why I'm not getting
>     values.
>     > > However, my ultimate goal is to obtain monthly gas usage
>     values for
>     > > one boiler and 4 ovens for the facility I am modeling. Since I'm
>     > > trying to model a boiler and 4 ovens, could I just simply
>     specify the
>     > > total power input from the boiler and ovens (in watts) under
>     the GAS
>     > > EQUIPMENT object? When I did that, I got an error in my
>     simulation. Or
>     > > do I need to use the boiler object and something else for the
>     ovens?
>     > > I'm still struggling with trying to get gas usage values for
>     this part
>     > > of my work. Any help or suggestions would be appreciated.
>     > > >
>     > > > Thank you,
>     > > > Dimos
>     > > >
>     > > > --- On Mon, 7/28/08, JV Dirkes II <jvd2pe@> wrote:
>     > > >
>     > > > From: JV Dirkes II <jvd2pe@>
>     > > > Subject: [EnergyPlus_ Support] Re: need help w/ monthly gas
>     usage
>     > results
>     > > > To: EnergyPlus_Support@ yahoogroups. com
>     > > > Date: Monday, July 28, 2008, 12:48 PM
>     > > >
>     > > >
>     > > >
>     > > >
>     > > >
>     > > >
>     > > > Dear Dimos,
>     > > >
>     > > > I took a look at your file and I think your problem is this:
>     > > >
>     > > > 1) You have an ELECTRIC heating coil in the furnace.
>     > > > 2) Since the Furnace is the only heating object, and its
>     coil uses
>     > > > electricity, there is no load for the Boiler:Steam.
>     > > > 3) Therefore, there is no gas consumption.
>     > > >
>     > > > --- In EnergyPlus_Support@ yahoogroups. com, "ellinas.1984"
>     > > > <ellinas.1984@ ...> wrote:
>     > > > >
>     > > > > Hello group,
>     > > > > The facility I am modeling has two boilers. I specified one of
>     them
>     > > > > under the boiler object in EnergyPlus just to see how it would
>     > run. I
>     > > > > also specified the gas rate schedule. However, when I run the
>     > > > > simulation and view the results, I get values of zero for the
>     > monthly
>     > > > > gas usages. Unlike the results from the electricity rate
>     schedule
>     > > that
>     > > > > I specified, where it shows the monthly usage in the results,
>     I get
>     > > > > nothing for the gas. Is there anyone out there that knows
>     how to
>     > help
>     > > > > me solve this problem?
>     > > > >
>     > > > > Thank you,
>     > > > > Dimos
>     > > > >
>     > > > > p.s. I uploaded my idf file. It is bakery3.idf with the
>     subtitle
>     > "gas
>     > > > > rate usage values" under the problem submittal folder.
>     > > > >
>     > > >
>     > >
>     >
>
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/