You certainly don’t have to “implement
code,” but you would have to dig into the text-based input file for EnergyPlus
and do simulations outside of DesignBuilder. You would need to modify the
input file, using text editor or IDFEditor, to add input objects called
Surface:HeatTransfer:ExteriorNaturalVentedCavity and Other Side Conditions
Model. These are explained in the Input Output reference. These are for opaque
facades, not glazed ones. From: Dear team, I am doing a simulation of ventilated
facades using energyplus and desingbuilder. I know that energyplus have
one method (ExteriorNaturalVen I know that itʼs not possible to simulate
this type of facades using desingbuilder, only using energyplus, but I know
that I can export the building from desingbuilder to energyplus and then
simulated the building using the method ExteriorNaturalVent Can anyone help me with this? Thank you, Catarina carvalhal P.S. sorry for the bad English The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.