[EnergyPlus_Support] PlantFlowResolver: Branch flow rates out of bounds
Dear All,
I developed a model with 13 zones and tired to use compact HVAC
VAV and FCU to feed those 7 zones and 6 zones respectively. However,
during simulation, it showed an error as shown below:
** Warning ** PlantFlowResolver: Branch flow rates out of bounds, for
Plant Loop=CHILLED WATER PLANT CHILLED WATER LOOP, Branch=VAV 1
COOLING COIL CHW BRANCH
** ~~~ ** Conditions should be: 886.834 <= 68.233 <= 92.188
Occurrence info=TIANJIN ANN CLG .4% CONDNS DB=>MWB, 07/21 08:00 -
08:15
** Severe ** FindRootSimpleController: Controller error for
controller = VAV 6 COOLING COIL CONTROLLER
** ~~~ ** Occurrence info=TIANJIN TIANJIN CHN CUSTOM-545270
WMO#=545270, 01/01 01:15 - 01:30
** ~~~ ** Controller function is inconsistent with user
specified controller action = Reverse action
** ~~~ ** Actuator will be set to maximum action
** ~~~ ** Controller control type=Temperature
** ~~~ ** Controller temperature set point = 12.29 [C]
** ~~~ ** Controller sensed temperature = 726.87 [C]
** ~~~ ** Controller actuator mass flow rate set to 125.96
[kg/s]
** ~~~ ** Controller actuator temperature = 735.61 [C]
This error occured at all branches of VAV and FCU. What should I do
to solve this problem?
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/