Re: [EnergyPlus_Support] Ventilation heat losses / gains



Ana:

Your observation is right. Results of the ventilation heat gain are not 
right. The problem is that the report variable of ventilation sensible heat 
gain was not initialized. The problem was raised after Version 2.2 release 
and was fixed for the next release (CR 7519). Results of the ventilation 
heat loss are correct. The workaround is to use infiltration objects instead 
of ventilation objects, since you don't use fan power.

Please let me know if you have any problems.

Lixing
----- Original Message ----- 
From: "Ana Rui Oliveira" <anarui.oliveira@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Tuesday, September 30, 2008 11:16 AM
Subject: [EnergyPlus_Support] Ventilation heat losses / gains


Hi.

Kind of urgently...

Any ideia why the ventilation heat gain in a Summer week (both sensible
and total) would be of a much higher order of magnitude than the
ventilations loss in a Winter week?

Ventilation is done using AirFlow»Ventilation objects with ero "Fan
Pressure Rise" and I'm just using Purchased Air to control
temperatures, so there shouldn't be any temperature rise due HVAC
components?...

I uploaded a file with some prt screens of these graphic results, to
facilitate interpretation.

Appreciate any help...
Ana.



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate 
folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the 
Documentation link and press the "search" button.
Yahoo! Groups Links





------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/