Re: [EnergyPlus_Support] Dual Minimum VAV Terminal Unit



The VAV boxes remain at the minimum flow in heating mode unless the 
heating coil is maxed out on heating capacity, then the air flow rate 
starts to increase. You might try reducing the size of the heating coil 
until the box starts to open.

Rosenberg, Michael I wrote:
>
> Is there any way to simulate a VAV terminal unit with dual minimum 
> positions? For example the minimum would be 20% during deadband 
> increasing to a maximum of 50% during reheat.
>
>  
>
> *__________________________*
>
> *Michael Rosenberg*
> Senior Commercial Buildings Energy Analyst
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg@xxxxxxx
> www.pnl.gov
>
>  
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/