Re: [EnergyPlus_Support] VAV max flow rate for heating



Yes: all input in System Sizing and Zone Sizing is used for sizing calcs only. It
doesn't affect operation during the actual simulation. As long as you have
VAV terminal units in your system with a minimum flow ratio less than 1.0 you will get
VAV action.

Fred Buhl

Danny Bishop wrote:

I do want it to run with variable volume. If I do this will it run variable volume?

Thanks

Danny

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Fred Buhl
Sent: Tuesday, 25 November 2008 4:26 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] VAV max flow rate for heating

 

In System Sizing, set "minimum system air flow ratio" to 1.0.

In release 3.0, this would be Sizing:System, "Minimum System Air Flow
Ratio".

Fred Buhl

bish.dj61 wrote:
> hi All
> For some reason I am getting a max air flow rate of the turn down ratio
> x the summer peak air flow rate when I use the "design day" method to
> size my VAV system for heating air flow rate. Shouldn't the max flow
> rate be the 100% flow rather than the fully turned down flow?
>
> cheers
> Danny
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

 

No virus found in this incoming message.
Checked by AVG.
Version: 7.5.549 / Virus Database: 270.9.9/1802 - Release Date: 20/11/2008 7:28 PM


No virus found in this outgoing message.
Checked by AVG.
Version: 7.5.549 / Virus Database: 270.9.10/1810 - Release Date: 24/11/2008 2:36 PM

__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___