Re: [EnergyPlus_Support] Re: Insufficient Vertex entries error message
X,Y,Z values for each corner. Yes you need 12 for a rectangle (just like
a typical wall).
irishhokie09 wrote:
>
> But I want a rectangular door, so I should have 12 entries, correct?
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Linda Lawrie
> <linda@...> wrote:
> >
> > Because each vertex is specified with an X,Y,Z set of 3 values.
> >
> > Ergo, to have a triangular door, you need 9 entries.
> >
> > Linda
> >
> > At 10:12 AM 12/2/2008, irishhokie09 wrote:
> > >When I try to run my simulation, the program crashes because of severe
> > >errors concerning doors which say:
> > >
> > >"GetHTSubSurfaceData: Insufficient number of vertex (autocalculate)
> > >entries for Surface="NORTH_DOOR7" must be >= 3. Only 4 provided."
> > >
> > >This message alone doesn't make much sense, but there are also warning
> > >messages for each of these severe errors that say:
> > >
> > >"GetHTSubSurfaceData: Number of vertex entries for
> > >Surface="NORTH_DOOR7" not even multiple of 3. Will read in 4"
> > >
> > >Does anyone know why doors have to have a multiple of 3 vertices?
> > >
> > >Thanks,
> > >Kevin
> > >
> > >
> > >------------------------------------
> > >
> > >The primary EnergyPlus web site is found at:
> > >http://www.energyplus.gov <http://www.energyplus.gov>
> > >
> > >The group web site is:
> > >http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/>
> > >
> > >Attachments are not allowed -- please post any files to the
> > >appropriate folder in the Files area of the Support Web Site.
> > >
> > >EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
> > >under the Documentation link and press the "search" button.
> > >Yahoo! Groups Links
> > >
> > >
> > >
> >
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/