[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Quadratic & Bi Quadratic



Ashok,

If you decide to use the coefficients as displayed on the chart then
make sure you include enough significant figures for each coefficient;
especially the coefficients of the higher powered variables.  You can
format the displayed numbers in the chart by right-clicking on the chart
equation box.

Michael L. Kingsley, PhD, PE, LEED AP
Senior Engineer/ Project Manager
SAIC

-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Richard Raustad
Sent: Wednesday, January 21, 2009 7:50 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Quadratic & Bi Quadratic

I use excel and the method described below. If by "polynomial curves" 
you mean adding a trend line to a plot and using the "Display equation 
on chart" option, then yes, that will work also (but only for Linear, 
Quadratic, or Cubic curves)..

ashok wrote:
>
> Thanks Richard info, is it possible get a coefficient by using excel 
> or polynomial curves,
> 
> 
> Regards
> Ashok
> 
>
> ----- Original Message -----
> *From:* Richard Raustad <mailto:RRaustad@xxxxxxxxxxxx
<mailto:RRaustad%40FSEC.UCF.EDU> >
> *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> 
> <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support%40yahoogroups.com> >
> *Sent:* Thursday, January 15, 2009 12:16 AM
> *Subject:* Re: [EnergyPlus_Support] Quadratic & Bi Quadratic
>
> It's pretty easy to create the coefficients for curve objects. You
> just
> have to set up a spreadsheet to look like the equation. I did not
> open
> the manufacturers data, but can give you an idea of how to go about
> this. The chiller EIR curve is the easiest to explain in an email.
>
> Set up spreadsheet data in columns according to the equation. For
> example a quadratic curve for energy input ratio (EIR) as a
> function of
> part-load ratio (PLR) would look like this:
>
> ChillerEIRfPLR = a0 + a1(PLR) + a2(PLR)(PLR)
>
> Here is an example set of data:
> Full load power at the rating point = 10 kW (PLR = 1)
>
> The following data is for the same entering condenser temp and
> exiting
> evaporator temp as the rating point
>
> Power at PLR of 0.7 = 6.5 kW
> Power at PLR of 0.5 = 4.0 kW
> Power at PLR of 0.3 = 2.5 kW
>
> Normalized power (EIR) at a PLR of 1.0 = 1.00 (10 kW / full load
> power
> of 10 kW)
> Normalized power (EIR) at a PLR of 0.7 = 0.65 (6.5 kW / full load
> power
> of 10 kW)
> Normalized power (EIR) at a PLR of 0.5 = 0.40 (4.0 kW / full load
> power
> of 10 kW)
> Normalized power (EIR) at a PLR of 0.3 = 0.25 (2.5 kW / full load
> power
> of 10 kW)
>
> Then set up the columns in a spreadsheet to look like your equation:
> EIRfPLR PLR PLR*PLR
>
> I used periods below instead of spaces so the data would line up
> better
> in the yahoo email
>
> Column
> ..A........ B.......C
> 1.00....1.00....1.00
> 0.65....0.70....0.49
> 0.40....0.50....0.25
> 0.25....0.30....0.09
>
> Then use the tools menu and select "data analysis". Choose regression
> from the list of choices (if you do not see data analysis you will
> have
> to install it from the original CD)
>
> Select column A as the Y range and both columns B and C for the X
> range.
> DO NOT check the box "crosses at zero". Select the output range in
> your
> spreadsheet (a blank area) and click OK.
>
> You will then get the coefficients a0, a1, and a2.
>
> mahesh_bara wrote:
> >
> > Dear All
> >
> > I have atached folder called quadratic & Biquadratic.
> >
> > I dont know how to create quadratic and biquadratic coefficent
> from the
> > chiller data sets given
> >
> > Would be great help if you can send us the details
> >
> > Regards
> > Mahesh
> >
> >
>
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
<http://www.fsec.ucf.edu> 
> <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu> >
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>


UCF - From Promise to Prominence: Celebrating 40 Years



 

------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/