There is some incorrect information in
this post. “U-value” per se does have a well-defined meaning
in the context of fenestration product rating (e.g. vertical orientation, solar
at normal incidence, standard winter/summer conditions), but during the EnergyPlus’s
timestep calculations, the tilt and solar incidence angles make a big a
difference. In E+, window performance is a function of tilt for
convection calculations both inside the glazing cavities (see ISO 15099) and
along the room-siden of the window or skylight. The implications of tilt
and solar beam incidence angle are as documented in the engineering reference
section “Calculation of Angular Properties”. From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Tasos Ioannou
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.