Thanks a lot for the quick help! my simulation timestep is indeed
hourly, and timesteps per hour are 4. 
And I will have a look at the hybrid ventilation as well.
regards,
Astrid


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> Astrid:
> 
> The answer to the first question (Tzone< 22C and windows are open)
is that 
> the report frequency may be hourly, instead of "detailed". The 
> AirflowNetwork model works at every system time step, which is equal
or less 
> than the zone time step given in the input file. When the report
frequency 
> is greater than the system time step, the average airflows are
reported. It 
> is possible that the zone temperature may be higher than 22C in a
system 
> time step during the report frequency, so that you may see airflows
or other 
> report variable values are not zero due to average.
> 
> The answer to the second question is that you may try to use the 
> AvaiabilityManager:HybridVentilation object. One of purposes for
this object 
> is to prevent simultaneous natural ventilation and HVAC system
operation. 
> The detailed descriptions are given in both Input Output Reference and 
> Engineering Reference. An example input file, called 
> HybridVentilationControl.idf, may give a guide how to use this object.
> 
> Please let me know if you need more information.
> 
> Thanks.
> 
> Lixing
> ----- Original Message ----- 
> From: <astroid8@...>
> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Tuesday, March 03, 2009 10:52 AM
> Subject: [EnergyPlus_Support] airflow network influenced by zone
controls? 
> ventilation setpoint does not work
> 
> 
> Dear all,
> 
> I got stuck with two questions regarding the airflow network system:
> 
> I am modelling an airflow network system for natural ventilation,
> using the ventilation control mode "temperature". my setpoint
> temperature above which the windows should be modelled open is 22°C.
> However if I look at the output (zone/sys air temperature) I can also
> find hours with opened windows even if the zone temperature is
> slightly below 22... What is my mistake?
> 
> Additionally I want to calculate the cooling loads to a certain
> setpoint, so I use dual setpoint with deadband at zone control
> thermostatic. How is it possible to switch off the natural ventilation
> (i.e. assume closed windows) defined in airflow network system while
> the cooling system is running?
> 
> I would be happy about some help,
> 
> Regards, Astrid
> 
> 
> 
> ------------------------------------
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate 
> folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf
under the 
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/