|
I am receiving the following error:
GetZoneEquipmentData1: Number of Zone Equipment lists
[2] not equal Number of Controlled Zones [1]
** ~~~ ** ..Each Controlled Zone must have a corresponding (unique) ZoneHVAC:EquipmentList ** Fatal ** GetZoneEquipment: Incorrect number of zone equipment lists ...but I
don't see the problem here (unless
its somewhere else!?):
ZoneHVAC:EquipmentConnections,
108, !- Zone Name 108Equipment, !- Zone Conditioning Equipment List Name 108 PTHP Supply Inlet, !- List Name: Zone Air Inlet Nodes 108 PTHP Return, !- List Name: Zone Air Exhaust Nodes 108 Zone Air Node, !- Zone Air Node Name 108 Return Outlet; !- Zone Return Air Node Name ZoneHVAC:EquipmentList,
108Equipment, !- Name ZoneHVAC:PackagedTerminalHeatPump, !- Zone Equipment 1 Object Type 108 PTHP, !- Zone Equipment 1 Name 1, !- CoolingPriority 1; !- HeatingPriority ZoneHVAC:PackagedTerminalHeatPump,
108 PTHP, !- Name HVACTemplate-Always 1, !- Availability Schedule Name 108 PTHP Return, !- Air Inlet Node Name 108 PTHP Supply Inlet, !- Air Outlet Node Name 108 PTHP OA Mixing Box, !- Outdoor Air Mixer Name autosize, !- Supply air volumetric flow rate during cooling operation {m3/s} autosize, !- Supply air volumetric flow rate during heating operation {m3/s} , !- Supply air volumetric flow rate when no cooling or heating is needed {m3/s} autosize, !- Outside air volumetric flow rate during cooling operation {m3/s} autosize, !- Outside air volumetric flow rate during heating operation {m3/s} autosize, !- Outside air volumetric flow rate when no cooling or heating is needed {m3/s} Fan:OnOff, !- Supply Air Fan Object Type 108 PTHP Supply Fan, !- Supply Air Fan Name Coil:Heating:DX:SingleSpeed, !- Heating Coil Object Type 108 PTHP Heating Coil, !- Heating Coil Name 0.001, !- Heating convergence tolerance {dimensionless} -8, !- Minimum outdoor dry-bulb temperature for compressor operation {C} Coil:Cooling:DX:SingleSpeed, !- Cooling Coil Object Type 108 PTHP Cooling Coil, !- Cooling Coil Name 0.001, !- Cooling convergence tolerance {dimensionless} Coil:Heating:Electric, !- Supplemental Heating Coil Object Type 108 PTHP Supp Heating Coil, !- Supplemental Heating Coil Name autosize, !- Maximum supply air temperature from supplemental heater {C} 21, !- Maximum outdoor dry-bulb temperature for supplemental heater operation {C} DrawThrough, !- Fan Placement HVACTemplate-Always 0; !- Heat pump operating mode __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |