You're referring to the .DDY file that is in the .ZIP on
the weather data page. For those locations that have data in the ASHRAE
2005 Fundamentals, there are many combinations of annual percentile design days
-- identified in the title. The first six are annual heating design
conditions -- either drybulb temperature, humidification or wind
speed:
! SAO_PAULO/CONGONHAS_BRA Annual Heating 99.6%,
MaxDB=8.8°C
! SAO_PAULO/CONGONHAS_BRA Annual Heating 99%,
MaxDB=10°C
! SAO_PAULO/CONGONHAS_BRA Annual Humidification 99.6%
Design Conditions DP=>MCDB, DP=3.9°C
! SAO_PAULO/CONGONHAS_BRA Annual Humidification 99%
Design Conditions DP=>MCDB, DP=5.8°C
! SAO_PAULO/CONGONHAS_BRA Annual Heating Wind 99.6%
Design Conditions WS=>MCDB, WS=7.9m/s
! SAO_PAULO/CONGONHAS_BRA Annual Heating Wind 99%
Design Conditions WS=>MCDB, WS=6.8m/s
The next twelve are annual cooling design conditions --
either drybulb temperature, wet-bulb temperature, dewpoint temperature, or
enthalpy at three percentiles:
! SAO_PAULO/CONGONHAS_BRA Annual Cooling (DB=>MWB)
.4%, MaxDB=32°C MWB=20.3°C
! SAO_PAULO/CONGONHAS_BRA Annual Cooling (DB=>MWB) 1%, MaxDB=31°C MWB=20.4°C ! SAO_PAULO/CONGONHAS_BRA Annual Cooling (DB=>MWB)
2%, MaxDB=30°C MWB=20.4°C
! SAO_PAULO/CONGONHAS_BRA Annual Cooling (WB=>MDB)
.4%, MDB=27.6°C WB=23.2°C
! SAO_PAULO/CONGONHAS_BRA Annual Cooling (WB=>MDB)
1%, MDB=27.1°C WB=22.6°C
! SAO_PAULO/CONGONHAS_BRA Annual Cooling (WB=>MDB)
2%, MDB=26.7°C WB=22.1°C
! SAO_PAULO/CONGONHAS_BRA Annual Cooling (DP=>MDB)
.4%, MDB=25.3°C DP=22.1°C HR=0.0185
! SAO_PAULO/CONGONHAS_BRA Annual Cooling (DP=>MDB) 1%, MDB=24.3°C DP=21.2°C HR=0.0175 ! SAO_PAULO/CONGONHAS_BRA Annual Cooling (DP=>MDB) 2%, MDB=24°C DP=21°C HR=0.0172 ! SAO_PAULO/CONGONHAS_BRA Annual Cooling (Enthalpy=>MDB) .4%, MDB=27.6°C Enthalpy=73.5kJ/kg ! SAO_PAULO/CONGONHAS_BRA Annual Cooling (Enthalpy=>MDB) 1%, MDB=27.1°C Enthalpy=71.2kJ/kg ! SAO_PAULO/CONGONHAS_BRA Annual Cooling (Enthalpy=>MDB) 2%, MDB=26.7°C Enthalpy=69.2kJ/kg The ASHRAE 2005 Fundamentals also has monthly design
conditions for these types as well.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of André Ricardo Quinteros Sent: Thursday, March 12, 2009 2:47 PM To: energyplus_support@xxxxxxxxxxxxxxx Subject: [EnergyPlus_Support] weather file
Why the climate file Congonhas SWERA
IDF has 18 designday? the correct would be 12, containing all the months of
the year? appear only the months of February and July. Why did
not appears other months? Conheça já o Windows Live Spaces, o site de relacionamentos do Messenger! Crie já o seu! __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.