Thank you very much, with "detailed" it's correct. So it is not a mistake, and due to the time step.
Astrid
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Change your report variable output frequency from "hourly" to "detailed"
> and try again.
>
> astroiid wrote:
> >
> > dear all,
> >
> > I am simulating a simple office room, with one daylight reference
> > point (central) and stepped control (only on/off). My illumincance
> > setpoint is 500lux, however, there are hours where illuminance exceeds
> > 500lux, but lighting is switched on. What could be the reason? I am
> > using hourly outputs but simulation time step is 4, does that have
> > some influence?
> >
> > I would be happy about any help,
> >
> > Astrid
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/