Re: [EnergyPlus_Support] (unknown)
** Severe ** Shading:Site:Detailed Name, duplicate name=COLLECTOR
SURFACE 1
** ~~~ ** ...each surface name must not duplicate other surface
names (of any type)
You have 2 objects with the same name: Change the second one to
Collector Surface 2.
Shading:Site:Detailed,
Collector Surface 1, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
0.0, 1.718, 1.718, !- X,Y,Z 1 {m}
0.0, 0, 0, !- X,Y,Z 2 {m}
1.220, 0, 0, !- X,Y,Z 3 {m}
1.220, 1.718, 1.718; !- X,Y,Z 4 {m}
Shading:Site:Detailed,
Collector Surface 1, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
0.0, 1.718, 1.718, !- X,Y,Z 1 {m}
0.0, 0, 0, !- X,Y,Z 2 {m}
1.220, 0, 0, !- X,Y,Z 3 {m}
1.220, 1.718, 1.718; !- X,Y,Z 4 {m}
Ανδρέας Χριστοφόρου wrote:
>
> Thanks for the quick reply
> Here is the IDF and the err. file
>
>
> ------------------------------------------------------------------------
> Χρησιμοποιείτε Yahoo!
> Βαρεθήκατε τα ενοχλητικά μηνύ ματα (spam); Το Yahoo! Mail διαθέτει την
> καλύτερη δυνατή προστασία κατά των ενοχλητικών μηνυμάτων
> http://login.yahoo.com/config/mail?.intl=gr
> <http://login.yahoo.com/config/mail?.intl=gr>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/