Re: [EnergyPlus_Support] How to connect CW Supply Outlet Node with CW Demand Inlet Node
This IS the connection. These nodes will not actually connect together
in other objects.
yangchen19851226 wrote:
>
> PlantLoop,
> Chilled Water Loop, !- Name
> Water, !- Fluid Type
> CW Loop Operation, !- PlantEquipmentOperationSchemes Name
> CW Supply Outlet Node, !- Loop Temperature Setpoint Node Name
> 98, !- Maximum Loop Temperature {C}
> 1, !- Minimum Loop Temperature {C}
> autosize, !- Maximum Loop Flow Rate {m3/s}
> 0.0, !- Minimum Loop Flow Rate {m3/s}
> autocalculate, !- Plant Loop Volume {m3}
> CW Supply Inlet Node, !- Plant Side Inlet Node Name
> CW Supply Outlet Node, !- Plant Side Outlet Node Name
> Cooling Supply Side Branches, !- Plant Side Branch List Name
> Cooling Supply Side Connectors, !- Plant Side Connector List Name
> CW Demand Inlet Node, !- Demand Side Inlet Node Name
> CW Demand Outlet Node, !- Demand Side Outlet Node Name
> Cooling Demand Side Branches, !- Demand Side Branch List Name
> Cooling Demand Side Connectors, !- Demand Side Connector List Name
> Sequential; !- Load Distribution Scheme
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/