Re: [EnergyPlus_Support] outdoor temperatures don't change when weather file changes
The "Run Simulation for Weather File Run Periods" must be set to Yes to
see the results for the weather file simulation. If this input is set to
NO, the simulation will always give the same answer based on the sizing
period objects which are fixed in the input file.
SimulationControl,
No, !- Do Zone Sizing Calculation
No, !- Do System Sizing Calculation
No, !- Do Plant Sizing Calculation
Yes, !- Run Simulation for Sizing Periods
No; <<<<<<<<<<<<< !- Run Simulation for Weather File Run Periods
SizingPeriod:DesignDay,
CHICAGO_IL_USA Annual Heating 99% Design Conditions DB, !- Name
-17.3, !- Maximum Dry-Bulb Temperature {C}
0.0, !- Daily Temperature Range {deltaC}
-17.3, !- Humidity Indicating Conditions at
Maximum Dry-Bulb
99063., !- Barometric Pressure {Pa}
4.9, !- Wind Speed {m/s}
270, !- Wind Direction {deg}
0.0, !- Sky Clearness
0, !- Rain Indicator
0, !- Snow Indicator
21, !- Day of Month
1, !- Month
WinterDesignDay, !- Day Type
0, !- Daylight Saving Time Indicator
WetBulb; !- Humidity Indicating Type
yangchen19851226 wrote:
>
>
> In my simulation with the file of airflownetwork3zvent,I don't know
> why the outdoor temperature and zone temperature don't change when
> weather file changes.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/