Re: [Bldg-sim] VAV fan energy



Dear Per Sahlin,
 
The simple fact is that fans which unload (those with variable inlet vanes , VSDs, etc.) do so in a way that is fairly represented by a curve.  The generic curves found in most energy analysis programs are reasonable representations of the unloading characteristics.  It is a good idea to have a library of typical curves if your energy analysis program of choice doesn't have such a library.
 
For a new building where your only purpose is to compare a "baseline" to your specific design, it's reasonable to use a generic curve.  This is because the actual operating conditions are not known for new construction; you know only the designer's best calculation, not the "as built" conditions.
 
For an existing building where you want to establish a model that represents the actual conditions as closely as possible, it's probably worth developing specific, custom curve coefficients for the installed fan(s).
 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

 


From: bldg-sim-bounces@xxxxxxxxxxxxxxxxxxxxx [mailto:bldg-sim-bounces@xxxxxxxxxxxxxxxxxxxxx] On Behalf Of Per Sahlin
Sent: Wednesday, April 29, 2009 10:46 AM
To: bldg-sim@xxxxxxxxxxxxxxxxxxxxx; EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [Bldg-sim] VAV fan energy

Hi all,

 

In E+, ASHRAE standard 90 (App. G)  and in some other places, fan power  for VAV systems with variable speed drives is modeled as a given function of part load ratio. I think the theory behind this originally comes from BLAST. This must be based on assumptions for the shape of the fan efficiency curve and on the pressure characteristic and control of the VAV system. Does anyone have access to the original theory on this? Alternatively, can anyone explain why and when the “single curve for all fans and systems” approach works?

 

Best regards,

 

Per Sahlin