|
The DX coil model tests the available capacity with the coil off and then with the coil on to get the "No load" and "Full load" capacities used for determining PLR. This means that if the DX coil does not need to operate, the warning will be tripped even though the coil is off. This will be corrected in a future version of EnergyPlus. For now, report the DX coil air inlet node temperature and compressor PLR to see if the DX coil is actually on when the inlet temperature is below 2C (you may need to use a detailed reporting frequency if the air temperature is very close to 2C when the DX coil operates). If the DX coil is not operating when the air temperature is below 2C, disregard the warnings. If the DX coil is actually on, you can count the number of times the coil operates below 2C. khaysepro wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |