Re: [EnergyPlus_Support] LEED EA Credit?



I hope the following responses help you:

1. Search the documentation (EPlusMainMenu.pdf) for "Demand 
Controlled Ventilation" and look for the object 
Controller:OutdoorAir

2. EnergyPlus does not currently provide the LEED EA Credit 
1 forms but does provide most of the values needed on the 
forms in the predefined reports.

3. The AppGPostProcess utility is documented in the 
AuxiliaryPrograms.pdf file and can be accessed using 
EP-Launch on the utility tab. It averages four runs together 
but at this point you have to rotate the building four 
times. I suggest using the Compliance:Building object with 
the Building Rotation for Appendix G field.

On 5/19/2009 11:43 PM, Sanjay wrote:
> How do i do the following?
>  
> EnergyPlus Version 3.1 
> Demand Control Ventilation model based on ventilation rate procedure of Standard 62.1-2007 procedure of Standard 62.1-2007.? 
> Output :LEED EA Credit 1 forms.? 
> averages the results from four building rotation runs for Standard 90.1 Appendix G compliance.?
> 
> 
> 
> 
> 
> 
> ------------------------------------
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
> 
> 
> 

-- 
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/