Re: [EnergyPlus_Support] Crack + natural Ventilation



Rich is correct. I would like to add more to make what you want.

You can use ventilation availability schedule to determine when you  
want a window be open or close in an AirflowNetwrok:Multizone:Surface,  
where a window opening object belongs. The window opening object can  
be AirflowNetwrok:Multizone:Comnponent:DetailedOpening. The object  
allows you to specifiy a relationship between airflow and pressure  
when a window is open and close.

Lixing
Quoting Richard Raustad <rraustad@xxxxxxxxxxxx>:

> I believe the answer is yes. But when the window is open, the
> ventilation through the cracks will be very near 0, or 0.
>
> v s wrote:
>>
>>
>>
>> Hi all,
>>
>> Can i have simultaneously from an Airflow Network, linkage through
>> cracks at windows (which is continuous) and night ventilation by
>> opening the windows?
>>
>> Thank you
>>
>> Vaggelis
>>
>>
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the   
> appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf   
> under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>





------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/