Re: [EnergyPlus_Support] Changing the capacity of an electric baseboard during the day
I would use 3 baseboards (800W, 1000W, 1500W) in the zone and use the
availability schedule for each baseboard to "schedule" the one you want
at specific times.
For example:
ZoneHVAC:Baseboard:Convective:Electric,
Baseboard1, !- Name
BBAvailabilitySchedule2, !- Availability Schedule Name
1000, !- Nominal Capacity (W)
Schedule:Compact,
BBAvailabilitySchedule2, !- Name
AnyNumber, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
FOR: AllDays, !- Field 2
UNTIL: 8:00, 1, !- Field 4
UNTIL:12:00, 0, !- Field 6
UNTIL:14:00, 1, !- Field 8
UNTIL: 24:00, 0; !- Field 10
le_carambar wrote:
>
>
> Hi,
>
> I would like heat a zone with one electric radiator. I achieved
> control it with a thermostat and now I would like control it myself.
> It means I would like specify it capacity during the day.
>
> A fictive example :
> 00:00 - 08:00 -> 1000W
> 08:00 - 12:00 -> 1500W
> 12:00 - 14:00 -> 1000W
> 14:00 - 24:00 -> 800w
>
> Have you an idea ?
>
> Thank
>
> Camille T.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/