When you are using a water system, please look up the
DistrictHeating, DistrictCooling
These are the equivalent objects to the Purchased Air for an air system.
For example, for heating:
DistrictHeating,Purchased Heating,
NODE_30,NODE_29,
1000000;
=====================
Field: Name
This alpha field contains the identifying name for the district heating (i.e., purchased hot
water).
Field: Hot Water Inlet Node Name
This alpha field contains the identifying name for the district heating inlet node.
Field: Hot Water Outlet Node Name
This alpha field contains the identifying name for the district heating outlet node.
Field: Nominal Capacity
This numeric field contains the nominal demand (W) that the district heating will meet
=================
You can get the followings as output for the above:
HVAC,Average,District Hot Water Rate [W]
HVAC,Sum,District Hot Water Energy[J]
Zone,Meter,DistrictHeating:Plant [J]
Zone,Meter,Heating:DistrictHeating [J]
HVAC,Average,District Heating Rate[W]
HVAC,Average,District Heating Inlet Temp[C]
HVAC,Average,District Heating Outlet Temp[C]
HVAC,Average,District Heating Mass Flow Rate[kg/s]
(from I/O Ref Manual)
If the number 1000000 is too small, the zone temperature setting will not be met. The maximum zone demand is available after a DesignDay sizing run.
You can set the zone temperature to vary during the day, and watch the demand changes. Set the timestep number higher to see more details on a DesignDay simulation.